The neighbours house is exactly 230V.
My house has 229v.
Measured at a plug: phase to ground is 113.5 and 113.8.
But another plug is 227.8 but the phases are 131 and 133
And there is 50V between the "unconnected" earth and the "unconnected" neutral... WTF?
Also 30V between either of these two "unconnected" wires and my new earth...
There is 50 amp limit, but that's still a shitboat full of energy.
The installation and wiring is from 1954 but the box and the differentials are 10 years old max.
I'll look around for the name of the electrician of the previous owner and report him, this is ridiculous.
"Angrier than this emoticon; "
I will now switch off the electricity and go cap those faaaackin' wires.
If you are measuring at a normal domestic power socket,(what we call a General Purpose Outlet,or
"GPO" in Oz),229 volts between the two
"non-Earth" pins is about right for a European system.(you are usually on the low side of "nominal"--we are on the high side).
Remember,those pins of a
GPO are not "Phase to Phase"------they are "One Phase & Neutral".
"Phase to Phase" would be around 400v.
It is not common in Domestic situations in Australia to bring 3Ph out to any sockets,it is usually used for stoves,hotwater systems,etc.or to feed two or more runs of GPOs,or light circuits.
I would suggest normal practice in your country would be similar.
It looks like you do not have a connection between Neutral & Earth at your Entry Point
Many of your funny results are because of this,AND the fact your DMM has a 11MegOhm input impedance-------------Google "Phantom Voltages",
,