Thank you Cliff, I watched some of the videos by Joe and was surprised how the glass fuses held up when connected directly across the mains.
I emailed Littelfuse with regards to some of my questions, below are their responses in red:
Would all ceramic fuses be considered a HRC fuse? No. To my understanding, the ability of a fuse to with withstand a high current fault without exploding/arcing can be considered HRC. No. A fuse operating safely within its interrupting capability is not necessarily considered to be HRC. If this is the case, would this high current fault be the fuses interrupt rating (aka breaking capacity) ? If so, what is the interrupt rating value for such a fuse to be considered HRC (i.e. 1.5kA? 10kA?) ? A High Rupture Capacity fuse is defined by the specification that was used for its design. For European IEC 60127 miniature fuses, HRC is defined as 1500A at 250VAC. This is the interrupt rating of the fuse.
As an electronics hobbyist sometimes I need to select a fuse that will be connected to the mains (120V AC). As part of the decision on selecting the fuse how do I decide on the correct interrupt rating. Some of my Little Fuses that I have specify an interrupt rating of 1.5kA at 250VAC. From my understanding the interrupt rating of the fuse should be higher than the prospective short circuit current:https://en.wikipedia.org/wiki/Prospective_short-circuit_current Yes, that is correct. If the short circuit current exceeds the fuse AIC (AmpInterrupting Capacity) rating, the fuse body might crack or shatter.
In this case I am assuming that my fuses interrupt rating needs to be rated higher than the prospective short circuit current that could occur at my residance before the circuit breaker trips? That is true, but residential wiring, switches, plugs, etc., normally has substantial resistance that will limit available short circuit current. If this is the case, would you know what the prospective short circuit current is for the general house in the United States? Not really sure. Much depends upon the physical location of the delivery point.
Follow up email:
I always thought only ceramic fuses could be HRC. Technically, any material can be used but ceramic is the usual material chosen. Fiberglass and Melamine also used. Based on the information you provided I understand now that HRC is "defined by the specification that was used for its design"
If I understand correctly, if there is a glass miniature fuse with an interrupt rating of 1500A at 250VAC then it too would be defined as an HRC fuse per IEC 60127 ? Yes, but there is no glass that can withstand the abuse so ceramic is normally used with a quartz sand filling