Well that's kind of silly.
Your outlets are clearly designed to shift up to 10A or so minimum so any current less than that is going to not cause the breakers to trip otherwise every time you run your vacuum cleaner it will pop the breakers.
Thus if you put that Antex iron into a socket, and it develops a fault that causes it to consume less than 16A but more than the rated (say insulation breakdown somewhere in the element which is quite common), the breaker will go after your soldering iron catches fire and burns down your house while quite happily sitting there sucking 7A or so.
Where as BS1363 typically includes a 3A fuse in such devices in the plug which limits the overall fault current of the device connected to the plug to 3A. Most "better than consumer crap" devices also have fuses in the device as well and IEC leads so most of the time we have say a 5A rated IEC lead and then a 100mA fuse in the device.
More protection is better than none.
To note my house is wired in a star topology as well, other than the lighting. A lot of newer houses and refurbished houses are in the UK.