In North America we have single phase for residential and 3 phase for commercial/industrial. In Canada, 3 phase is most commonly available as either 208/120Y or 600/347Y (delta/wye voltages). A friend moved his cabinet shop from a building with 600/347Y to 208/120Y. Some of his machines operated on 600/347Y and so the electrician connected some of my friend's step-down transformers as step-up transformers.
One transformer was quite hot even when unloaded and one day it blew its primary fuses - 100 A and north of $100 each. I measured the line voltages and currents and saw that the current was a lot higher than it should have been. On a hunch, I measured the neutral current at 50+ A when the transformer was unloaded. I disconnected the neutral and the line currents dropped down to a few amps and the transformer cooled right down.
3-phase distribution transformers are usually delta primary & wye secondary. It allows the secondaries to be re-referenced to neutral to prevent a circuit from floating. The electrician, true to code, tied the neutral of the transformer secondary to system neutral, but that's a no-no in this case. The delta-wye transformer configuration also eliminates negative sequence currents - this is where 3rd harmonic currents produce currents within the transformer that run opposite to the fundamental current. It not only detracts from the power delivered to the load but it causes I^2R losses. When reversed, the transformer doesn't block this current. It seems too that any voltage imbalance will also manifest as a neutral current.
The electrician probably knew better but this is what his customer wanted so he did what he was paid to do. I don't know the code well enough to say if he violated it but, in the end, you canna deny the laws of physics. I suppose the wiring was safe, it just wasted power and fuses.
I measured the secondary voltages (600/347Y) to earth/ground and saw they were about 350 V. I figure that if there's primary to secondary leakage, the maximum voltage won't be all that much higher than usual, ie. maybe 800 V instead of 600 V