So far so good
I reckon VFD may be fine with a 30ma RCD because the transformer should block all any recycling nasties going up and down the line/s causing issues
FWIW a good quality '30ma' labelled RCD should trip anywhere (depending on ambient conditions) between 22ma and 27ma in zero and 180 degree testing, or a real world trip
If 30ma is a fail, better to have a 100ma RCD than no RCD
I have one packed in a box somewhere
just in case, or as a future upstream RCD at the switchboard before the main breaker/isolator if ever needed
Doesn't hurt to own one, and not cheap or easy to get when you need one