Well, the blast is typical of an old paper insulated cable failing, probably due to water ingress from a corroded lead sheath on a joint, or the cast iron sheath corroded a pinhole. They can and do excavate themselves in the half second or so it takes for the MV circuit breaker to trip out, as those are designed to have a slight delay so they do not trip out when you power on a cold load after either a power failure or after it has tripped out due to a fault. Cable and switchgear is designed to survive the heating longer than it takes to trip out again, to isolate the fault, not to limit arc damage.
I have seen them dig a hole in the road 6m deep, as that is how deep the join was when the 33kV line failed early one morning. road was closed, seeing as there was no more lane either way, and the pavements were somewhat damaged as well by the blast.
Funny thing is 11kV cabling is a lot faster on protection, the guy with the pickaxe from Digotel (the colloquial name for the fibre layers, who are capable of finding every water pipe, cable and phone line in the road it seems) just had a wake up call, and a 1cm bite in the tip of the pick axe he put through the joint.