Author Topic: YH-305D Power Supply calibration procedure.  (Read 4698 times)
Offline Kaptein QKTopic starter
« on: April 24, 2013, 11:31:34 pm »
Here is a calibration procedure for the front panel meters:
Potmeters (See picture, the blue ones) left to right:
1- mA range gain.
2- A range gain.
3- mA and A offset.
4- V gain.
Current:
1: Set power supply to mA range.
2: Connect ampere meter.
3: Set current to approx 1mA. (because the front panel meters does not show negative)
4: Adjust current offset potmeter to let front panel show 1mA.
5: Set current to 990mA.
6: Adjust mA range gain potmeter let front panel to show 990mA.
7: Repeat step 3-6 until satisfied.
8: Set power supply to A range.
9: Set current to 4.90A.
10: Adjust A range potmeter let front panel to show 4.90A.
Voltage:
11: Set voltage to 30 V.
12: Adjust voltage gain potmeter to let front panel show 30V.
I could not find anything about calibration of this power supply on the net, so I started fiddling with the pots.
Hope it is useful for someone.
« Last Edit: April 24, 2013, 11:35:24 pm by Kaptein QK »
Offline jimw
Re: YH-305D Power Supply calibration procedure.
« Reply #1 on: February 04, 2017, 11:19:09 pm »
Thanks for posting this!  I did a similar exploration (before I found your post) and had figured out 3 of the 4 pots.  Got voltage and low range current pretty close, but was tired and quit before trying the high range.  Now I know which pot to twiddle when I open it up again.  :)
I assume your "left to right" meant from looking at the front of the supply.  As pictured from the inside, your numbers 1-4 go from right to left.
Thanks!
Jim
« Reply #2 on: November 04, 2017, 02:23:09 pm »
It is left to right as pictured.