| spiff72:
I took another stab at this tonight. This is the cleanest looking FFT I could get and fill the screen with a reasonable Hz/div value (100). In order to get this, I actually used "Memory" instead of "Trace" for the FFT, but to get a reasonable horizontal scale, I had to drop the memory depth to 12K points. Timescale is 50ms/div. I noticed that this one did NOT have the odd non-harmonic 700Hz peak. I then reloaded the settings from yesterday (via a saved settings file), and this is the second image. |
| spiff72:
Well, I did a test over the weekend and plugged the scope into an outlet near my panel and set up my probe to test the line voltage. I then shut off every breaker in the house except for one that feeds the circuit I was plugged into. The result was that there was no difference in the signal. so I have concluded that one of the following two statements is true: - The source of the distortion is outside the house (already present on the incoming feed) - The source of the distortion is on the same circuit that I had powered up to check I didn't get a chance, but I might re-run this test one more time to rule out a couple of additional doubts that came to mind after the test. - I was using the "averaging" method of the scope during the test (under the acquire menu). This could have possibly slowed the response time of the scope, but I doubt it. I might repeat in high-res or normal mode. - Plug scope into a different circuit to rule out that last circuit as the source of the distortion. - I also want to re-capture the waveform and FFT plot for the "before" and "after" shutting off all breakers. I did this, but lost track of which was which because the scope doesn't have a RTC to put a proper timestamp on the captured files. At the end of the day, if the source is not in the house, do i have any leverage with the power company to request they clean up the power coming into my house? Is it even anything to be concerned about? Thanks again! |
| Ragnarok:
3rd harmonics is generally from unbalanced 3 phase load. The transformer in the street is usually 3 phase (with households tapping different Phase + Neutral) 5th/7th/11th/13th harmonics are generally from rectifiers. Rectifiers will generally have harmonics generated on the (6n +/- 1) fundamental, where N is based on the topology of the rectifier design. Usually these harmonics are probably stray and seeps through the network, possibly from industrial customers connected on the local grid. |
| soldar:
This is what mine looks like: |
| Navigation |
| Message Index |
| Previous page |