| hgg:
"1kA or so of PSC" and not even the smallest spark on the multimeter leads? |
| Cnoob:
I look at Bussmann's graph for that particular fuse which is call a clearance graph of time v current. Assuming I reading the graph right. I'm reading that graph as the time taken for the fuse to clear a fault condition and as this was a short circuit near instantaneous currents are involved. How high ? it depends on your impedance of your voltage source. I think it's safe to assume it's a high current and on the graph. A near instantaneous current of 150 Amps the fuse will act in 15mS. I suspect the fuse could act quicker but Bussmann are erring on caution. So it is quite possible for that fuse to blow before the RCD can trip. |
| dmills:
Yep, RCDs are not (Unless RCBOs) overload sensitive, they will pass a lot of current and merely get hot, overload protection is a different type of breaker. I would expect a LOT more then 150A in a dead short to 'earth' situation assuming TN-C-S or TN-S supplies are in use (TT, the fuse might not even have blown in a week! This is NOT a good thing!). Like I say, THIS is why good multimeters have expensive fuses, quite possible a kA or so flowed, but probably the only part that failed was the fuse, and it kept all the damage contained inside the fuse housing, quite impressive actually. Regards, Dan. |
| hgg:
Do you think that not seeing any sparks was expected ? |
| IanB:
--- Quote from: hgg on March 07, 2019, 12:48:21 pm ---"1kA or so of PSC" and not even the smallest spark on the multimeter leads? --- End quote --- --- Quote from: hgg on March 07, 2019, 03:39:54 pm ---Do you think that not seeing any sparks was expected ? --- End quote --- You tend to get more of a spark when breaking a circuit than when making it. I have shorted 240 V mains a couple of times in the past, and it was not very dramatic. I hardly noticed I'd done it until afterwards, when the fuse had blown or the breaker had tripped. Each time I had just barely touched a live wire against a grounded terminal and that was enough to trip the circuit protection. |
| Navigation |
| Message Index |
| Next page |
| Previous page |