If I have a 240 vac 40 amp load can I protect it with a single pole 40 amp breaker on one leg of the 240 vac?
Title: Re: Circuit breaker question
Post by: Monkeh on June 24, 2023, 12:49:50 am
Ponder the outcome of a ground fault on the unfused leg. And then hire an electrician..
Title: Re: Circuit breaker question
Post by: helius on June 24, 2023, 01:54:45 am
If using the common 120-0-120 North American split-phase power, you must use ganged two-pole circuit breakers on 240V circuits.
Title: Re: Circuit breaker question
Post by: WattsThat on June 24, 2023, 04:56:55 am
No. You need a two pole ganged breaker as mentioned and #8 awg wire. If you use 8/2 with ground, mark the white lead with black tape on both ends.

Ovens/Ranges/Dryers now require a GFCI breaker.
Title: Re: Circuit breaker question
Post by: JustMeHere on June 24, 2023, 05:25:28 am
You have to have two adjacent slots free to get 240 out of an American panel.