Electronics > Beginners

Probing UPS inverter output with scope

<< < (2/2)

caspercba:
Thanks to eveyrone for their honest advices.

The UPS model is missing but i will have its model/brand tomorrow probably.
Mr. Swedish, don't worry, my  brother is not involved, so calm down. Thanks for your constructive? reply.

I don't think I will do the probing myself since it is dangerous but I wonder if the output of this ups , being of the online type ( fed 100% from batteries) could be proved with the probe ground .... In practice this would be like a battery powered device... Isn't it?

Cheers, again thanks for the quick advice!

roberts.tech:
I test inverters and ups units all week long at my company. I have a portable isolated Tektronix scope and I also use an old standard line operated scope on my bench. On the bench with the old scope I always make my measurements with a small 120 to 12 volt transformer to isolate the scope. I can see most of the problems right through this transformer such as distortion on the sinewave and the 40khz switching of the mosfet transistors if the output filter is not working well. For higher frequencies I have to switch to my digital isolated scope.
Yes the output of the your ups is derived from the battery but then the normal wiring conventions will be followed from there and it will be just like line voltage.
While it is possible to measure line voltage with a standard scope if you know what you are doing it is dangerous because of the lack of isolation. So I am not recommending it.
Get on ebay a buy a used portable scope like the Tektronix THS720A and you will have no worries.

David Hess:
I have no difficulty seeing the high frequency "steps" on the output of my sine inverters using a step down transformer to isolate the oscilloscope and this is where I would start just for safety.  There will not be any power line disturbances which would affect something without also being visible through a step down transformer.

A couple of times I set my oscilloscope to accumulate mode and monitored the output of an online UPS for days at a time but never detected any glitches which was as expected.

ferdieCX:

--- Quote from: caspercba on July 27, 2018, 03:26:25 pm ---
I don't think I will do the probing myself since it is dangerous but I wonder if the output of this ups , being of the online type ( fed 100% from batteries) could be proved with the probe ground .... In practice this would be like a battery powered device... Isn't it?


--- End quote ---

Almost for sure, the output of the UPS is wired with neutral, one or three phases and ground. It also has a Bypass relay that allows to feed the load direct from the distribution line, automatically in the event that the inverter fails, or manually for maintenance purposes.
The output of the UPS behaves like the distribution line of the power company.

Gregg:
Don’t lose sight of the bigger picture; that is the whole electrical power system from the utility power connection to the equipment that is intermittently failing.  Look for poor connections all along the way.  Check for voltage drop across breakers and especially transfer switches. 
There could be something like an air conditioning unit that sends a nasty inductive spike into the line ahead of the UPS.  Just because they use the word “uninterruptable” in the name doesn’t mean they have covered all possibilities.  If your father is running the lab, I’m sure he could have the UPS maintenance company check out the UPS.  For hospital situations I’m sure regular maintenance is a requirement.  UPS maintenance companies should have all of the testing equipment to safely test the high voltage output.  Try to be there when they do maintenance and try not to be a pest; most technicians are willing to explain things to a student that shows the right interest and asks intelligent questions.  Stay far back and quiet when they have the live high voltage open; respect the fact that there is zero tolerance for mistakes when working on live high voltage.
Another possibility is something connected to the output of the UPS injecting harmonics or spikes into the line, not the fault of the UPS.  What you really need is a power quality recorder instead of your scope.