I have a 25m rool/spool of 230v extension cable.
When using with high power utils (1000+ Watt) - I always make sure to unrool all of it.
Was once told about possible inductive kickback, if not doing that.
I'm no EE or Electrician , but i can run my devices wo. fuse blowing (10A).
I think 1800W is the max i have loaded it with.
Yes, I was suspicious of this effect of the rolled cable inductance play up when used with high current device pulling lots of currents through it.
I was not sure how it affects, and why in theory.
The cable should be unwound before using, especially to the full rating, but I repeat:
it's got nothing to do with the inductance. As I said before,
the currents in the neighbouring conductors flow in opposite directions, thus causing the magnetic fields to cancel each other out. Even if you put the live through one extension lead and the neutral through another (don't do this, it's a bad idea, it's just a thought experiment), so the fields don't cancel, the inductance would have a similar effect at 50 to 60Hz, as the resistance of the cable: a couple of mH inductance will have an impedance of just under an Ohm, similar to the DC resistance. The reason for this is because there's no magnetic core. This is why all transformers and inductors designed to work at mains frequencies have magnetic cores. Also note that inductance doesn't result an any power dissipation.
The reason for unwinding the cable is
purely thermal. A tightly wound coil concentrates the power dissipated due to I
2R losses in the cable, into a small space. The cable in the middle of the coil, doesn't have air circulating around it to provide convective cooling and any radiated heat is absorbed by a neighbouring turns, causing them to heat up more. When the cable is unwound, the heat can escape more easily due to better air circulation and the heat is able to radiate out into space more easily.
The bottom line is, a tightly coiled cable will heat much more, than an unwound cable, given everything else (current, length, conductor size) being equal. The temperature rating of the insulation will be exceeded, if it's not designed to work at full power, when coiled up, which is the case for all extension leads made.
Suppose the total resistance of the cable is 1 Ohm* and the current is 12A, P = I
2R, so that's a power dissipation of 144W, more than an old school 60W light bulb and a bit more than a slow cooker. Imagine the difference in temperature rise, when that heat is concentrated in a small area, compared to spread out over a large one.
*Based on 60m (the total length of the live + neutral in a 30m run) of 1.25mm
2 cable rounded up, given it's specified at 20
oC and the cable will get heat up.
http://www.farnell.com/datasheets/1805062.pdf