Hello,
The US National Electrical Code defines some restrictions about feeding an electrical panel from two sources (the utility grid and a local generator, like solar power).
The intent is to prevent the busbar from being overloaded.
The language is: "Where two sources, one a utility and the other an inverter, are located at opposite ends of a busbar that contains loads, the sum of 125 percent of the inverter(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed 120 percent of the ampacity of the busbar. "
In the following instead of "125 percent of the inverter(s) output" I'll just use "Generator breaker" - so that it'll be easier to follow
Let's start with a circuit where there there is no local generator. Here the main breaker will always protect the busbar, so there is no issue:
In the case we have a local generator and the breaker for the generator is located next to the main grid breaker, the restriction is taht grid breaker + generator breaker can't exceed busbar rating. This totally makes sense since you can easily overload the busbar, as follows:
Now, what doesn't make sense is if the generator is at the opposite side of the bus bar. NEC says that generator breaker + main breaker has to be max 120% of bus bar rating. I don't know how this makes sense or where the 120% comes from. To me seems obvious that it's OK to have both the main breaker and the generator breaker equal to the rating of the bus bar (and sum up to 200% of bus bar rating). Here is the scenario:
In the example above the bus bar is being fed with 200A from both directions. Even if the total load is 270A, no point of the bus bar would be carrying more than 200A at any time since if it did either the main breaker or the generator breaker would trip. The 270A would be split between the upper part and lower part of the bus bar. So, for example, the upper part (and therefore the main grid) would be carrying 170A and the lower part (generator) would be carrying 100A. The bus bar would not be overheating at any point - so what is the problem ?
Can anyone explain why the 120% rule exists and where the 120 number comes from ?