I was asked to measure the max DC input of a charging system, the DC input should be roughly 400v and no more then 800v. When I first measured the dc input it was 1265v. I tested 3 more times and the highest I recorded was 1663v. The manufacture said there was no way it could be that high. So I bought a Fluke 87v and a 1000:1 HV probe, and measured the site again. This time the manufacture flew their tech out to measure as well.
With the 1000:1 HV probe connected to the Fluke and the settings on Auto hold and the voltage range set to 6.000v
the results I got were 0.1114v. As I understand it that with using the 1000:1 HV probe that would equate to 1114v or would I be incorrect?
Thank you for your help with this