Author Topic: Is my 15KV neon light transformer broken ?  (Read 4420 times)

0 Members and 1 Guest are viewing this topic.

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Is my 15KV neon light transformer broken ?
« on: March 20, 2019, 01:24:17 pm »
Just scored this for free, and to be honest I was suspicious and curious why it's free ?  :-// But I couldn't measure it as I scored it while I was on traveling, so I paid just the shipping charge to send it back home.


With primary winding is rated for 220VAC at 2.25 Amp, while secondary with middle tap connected to chassis with 15KVAC at 30 mA, photo & details below.






Took out my LCR meter (4 W) and started to measure all windings with these results :



Question :

- Is it normal for the primary winding's DCR at that low ?  :-//

- Also while still on DCR mode, measured the resistance between primary vs secondary, the LCR meter showed infinite resistance, but sometimes once in a while flipped/flickered to 50 to 60 Mega Ohm reading, shorted inter-windings ?

« Last Edit: March 21, 2019, 08:31:57 am by BravoV »
 

Offline rsjsouza

  • Super Contributor
  • ***
  • Posts: 6106
  • Country: us
  • Eternally curious
    • Vbe - vídeo blog eletrônico
Re: Is my 15KV neon light transformer broken ?
« Reply #1 on: March 20, 2019, 01:33:58 pm »
I don't have my NST here to test, but 2.5 ohms on a 450VA transformer is not really unusual. The AC impedance would be higher.

The resistance between pri-sec is a bit more worrisome, but at those levels the ohmmeter can be very susceptible to external factors.

If you have a Variac, all your questions will be answered. :)
Vbe - vídeo blog eletrônico http://videos.vbeletronico.com

Oh, the "whys" of the datasheets... The information is there not to be an axiomatic truth, but instead each speck of data must be slowly inhaled while carefully performing a deep search inside oneself to find the true metaphysical sense...
 

Offline Fraser

  • Super Contributor
  • ***
  • Posts: 13524
  • Country: gb
Re: Is my 15KV neon light transformer broken ?
« Reply #2 on: March 20, 2019, 01:36:06 pm »
This thread may be of interest. You can calculate the inductive reactance of the primary.

https://www.physicsforums.com/threads/mains-transformer-with-1-4-ohm-primary-winding.924900/

HT transformers can arc across to the primary winding if they are not on separate bobbins and this used to happen in oscilloscope transformers. I would not expect a readable resistance at the voltage used in your meter test though. More likely it is your meter reading an infinite resistance and responding in an unpredictable way due to RFI etc.

If in doubt, connect a 240V 25W light bulb in series with the primary winding when first applying power to the transformer. If the secondary RCA’s over to the primary no great harm will occur. It is not uncommon for these Neon drive transformers or output connecting cable insulation to fail, causing the classic flickering Neon sign. Yours may well be OK.

Fraser
If I have helped you please consider a donation : https://gofund.me/c86b0a2c
 

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #3 on: March 20, 2019, 03:15:50 pm »
The resistance between pri-sec is a bit more worrisome, but at those levels the ohmmeter can be very susceptible to external factors.

Yeah, cause I was expecting pri-sec should have infinite resistance, but what external factors are you talking about ? As the transformer was not connected to anything except the LCR meter.


If you have a Variac, all your questions will be answered. :)

Start at really low voltage at primary using variac, and slowly crank up while measure the secondary ?

To be honest, all my meters are maxed out at 1KV, and quite scare as this is lethal voltage, still thinking how to properly isolate the output terminals before I start powering it.

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #4 on: March 20, 2019, 03:26:37 pm »
This thread may be of interest. You can calculate the inductive reactance of the primary.

https://www.physicsforums.com/threads/mains-transformer-with-1-4-ohm-primary-winding.924900/

Thanks for the link.

So, my primary reactance based on my measurements above ...

Reactance :
= 2 x pi x freq x inductance
= 2 x 3.14159 x 50 Hz x 0.414 Henry
= 130.06 \$\Omega\$

So at 220 VAC the primary current will be -> 220V / 130.06 \$\Omega\$ = 1.69A ?

Much lower than the rated current (2.25A) as printed at the label isn't it ? :-//


HT transformers can arc across to the primary winding if they are not on separate bobbins and this used to happen in oscilloscope transformers. I would not expect a readable resistance at the voltage used in your meter test though. More likely it is your meter reading an infinite resistance and responding in an unpredictable way due to RFI etc.

Are you saying at both isolated windings behave like sort of antenna, that caused that flickered high resistance reading as I experienced ?


If in doubt, connect a 240V 25W light bulb in series with the primary winding when first applying power to the transformer. If the secondary RCA’s over to the primary no great harm will occur. It is not uncommon for these Neon drive transformers or output connecting cable insulation to fail, causing the classic flickering Neon sign. Yours may well be OK.

Noted, will do, but as previous post, I will find a safe isolation caps 1st at that two HV terminals before powering this thing.

Also currently I don't have any HV probe to test it's output, really tempting to build an adhoc Jacob Ladder though, just to test it's output.  :palm:
« Last Edit: March 20, 2019, 03:29:28 pm by BravoV »
 

Offline chemelec

  • Contributor
  • Posts: 33
  • Country: ca
Re: Is my 15KV neon light transformer broken ?
« Reply #5 on: March 20, 2019, 04:45:54 pm »
I have Numerous Neon Transformers, but Being in Canada, they are all rated at 110 VAC for the Primary.
Here is a Picture of My Jacobs Ladder in Operation.
Look Closely and you can see the Arc.
 

Offline rsjsouza

  • Super Contributor
  • ***
  • Posts: 6106
  • Country: us
  • Eternally curious
    • Vbe - vídeo blog eletrônico
Re: Is my 15KV neon light transformer broken ?
« Reply #6 on: March 20, 2019, 05:12:12 pm »
The resistance between pri-sec is a bit more worrisome, but at those levels the ohmmeter can be very susceptible to external factors.

Yeah, cause I was expecting pri-sec should have infinite resistance, but what external factors are you talking about ? As the transformer was not connected to anything except the LCR meter.
As all LCR meters I know put out AC at various frequencies, any capacitive coupling may cause it to falsely read current flow, thus skewing the measurements.

Obviously that you can simply try to test with a regular DMM's ohmmeter (which only puts out DC) and see if you have any of such effects in your measurement.


If you have a Variac, all your questions will be answered. :)

Start at really low voltage at primary using variac, and slowly crank up while measure the secondary ?

To be honest, all my meters are maxed out at 1KV, and quite scare as this is lethal voltage, still thinking how to properly isolate the output terminals before I start powering it.
Exactly. Start at zero on the output of the Variac and increase it but never go over 14V.

For your transformer the turns ratio is 15.000V/220V = 68
The maximum input voltage then is: 1.000V/68 = 14V

The best way to experiment with this is across a very large area and clean of debris and other junk - if you want to do this on your bench, make sure it is clear of pliers, components, vises, screwdrivers, metallic boxes or plates, etc. Give wide clearance between wires on the high side and, if possible, keep them lifted off the ground. Don't rely on probes and use alligator clips on connections - you can also insulate these connections with insulating tape.

Once you get the high voltage bug, you can't shake it anymore off you.  :-DD
Vbe - vídeo blog eletrônico http://videos.vbeletronico.com

Oh, the "whys" of the datasheets... The information is there not to be an axiomatic truth, but instead each speck of data must be slowly inhaled while carefully performing a deep search inside oneself to find the true metaphysical sense...
 

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #7 on: March 21, 2019, 05:03:24 am »
If you have a Variac, all your questions will be answered. :)

Start at really low voltage at primary using variac, and slowly crank up while measure the secondary ?

To be honest, all my meters are maxed out at 1KV, and quite scare as this is lethal voltage, still thinking how to properly isolate the output terminals before I start powering it.
Exactly. Start at zero on the output of the Variac and increase it but never go over 14V.

For your transformer the turns ratio is 15.000V/220V = 68
The maximum input voltage then is: 1.000V/68 = 14V

Good idea, I think I have a small low wattage step-down transformer 220V -> 12V tucked somewhere, might be handy coupled with variac, thanks.  :-+


The best way to experiment with this is across a very large area and clean of debris and other junk - if you want to do this on your bench, make sure it is clear of pliers, components, vises, screwdrivers, metallic boxes or plates, etc. Give wide clearance between wires on the high side and, if possible, keep them lifted off the ground. Don't rely on probes and use alligator clips on connections - you can also insulate these connections with insulating tape.

Once you get the high voltage bug, you can't shake it anymore off you.  :-DD

Noted, yeah, HV bug, starting to worry about it too as this is my 1st venture at > 220V.  :-DD

Offline beanflying

  • Super Contributor
  • ***
  • Posts: 7375
  • Country: au
  • Toys so very many Toys.
Re: Is my 15KV neon light transformer broken ?
« Reply #8 on: March 21, 2019, 05:15:10 am »
Unplug anything sensitive EVERYWHERE get a few bits of heavy copper wire with a few bends 10-12mm gap opening up and then stand back and TEST ;D I ran an old scope on the Mains and a Clamp meter to check current and it was fairly clean and in spec so I am now less cautious when playing.

Mine is actually a 277V 60Hz Primary which runs fine on the local approx 250V 50Hz. Secondary was rated at 15kV so it will be down a bit.

Still planning to refurbish it and do something about safety of the ladder so it can be used in public lest any human smoke come out.

https://youtu.be/aGucgApUb64
« Last Edit: March 21, 2019, 05:16:54 am by beanflying »
Coffee, Food, R/C and electronics nerd in no particular order. Also CNC wannabe, 3D printer and Laser Cutter Junkie and just don't mention my TEA addiction....
 

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #9 on: March 21, 2019, 07:14:19 am »
Unplug anything sensitive EVERYWHERE get a few bits of heavy copper wire with a few bends 10-12mm gap opening up and then stand back and TEST ;D I ran an old scope on the Mains and a Clamp meter to check current and it was fairly clean and in spec so I am now less cautious when playing.

Mine is actually a 277V 60Hz Primary which runs fine on the local approx 250V 50Hz. Secondary was rated at 15kV so it will be down a bit.

Still planning to refurbish it and do something about safety of the ladder so it can be used in public lest any human smoke come out.

Damn, I think I got bitten by Jacobs Ladder bug, really, I didn't have any plan on this when I acquired it, as it was sitting gathering dust and was offered to me for free.  :palm:

I guess you mean refurbish it, just by remove the rust and re-paint the whole box only right ?

Cause I opened the top cover, the whole transformer and all it's wiring is sort of submerged completely into a solid hardened asphalt, looks like there is no simple fix if there is a problem inside, without getting the nasty work of removing that black thingy 1st, attached below how it looks inside.
« Last Edit: March 21, 2019, 08:03:49 am by BravoV »
 

Offline beanflying

  • Super Contributor
  • ***
  • Posts: 7375
  • Country: au
  • Toys so very many Toys.
Re: Is my 15KV neon light transformer broken ?
« Reply #10 on: March 21, 2019, 08:14:45 am »
Yep external Scrape and paint. Most of them are Bituminous filled or similar. I have already stripped and cleaned the terminals and insulators as much as possible as mine was well used.

A few basic cautions 15kV will travel over moist surfaces! Assume everything around the transformer can conduct when you are first testing it.

Play Safe  ;)
Coffee, Food, R/C and electronics nerd in no particular order. Also CNC wannabe, 3D printer and Laser Cutter Junkie and just don't mention my TEA addiction....
 

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #11 on: March 21, 2019, 08:18:34 am »
Obviously that you can simply try to test with a regular DMM's ohmmeter (which only puts out DC) and see if you have any of such effects in your measurement.

Update, tested using Fluke 189, manual range at Mega Ohm range, it started to flicker from infinite resistance to about > 200 Mega Ohm and slowly , I mean like at few seconds starting to crawl upward like 230 .. 240 ... 250 and so on.

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #12 on: March 21, 2019, 08:25:37 am »
A few basic cautions 15kV will travel over moist surfaces! Assume everything around the transformer can conduct when you are first testing it.

Play Safe  ;)

Thanks for the reminder, yeah, I will be very cautious and triple check at every connection made, and probably quadruple checks all over again before I power this thing. Also it will be put above a stool in the middle of the room, instead on top of bench table.

Waiting for my order to arrive of few meters of HV motor spark plug wire at local motorcycle repair/modding shop.

Offline Psi

  • Super Contributor
  • ***
  • Posts: 10385
  • Country: nz
Re: Is my 15KV neon light transformer broken ?
« Reply #13 on: March 21, 2019, 09:45:14 am »
if you're worried the primary might short you could put a resistive load in series with NST primary for the first power up.
A high wattage mains voltage incandescent lamp is a good load for this, if you still have one around somewhere.
If anything shorts out the lamp will just light up and nothing will go bang.

Note that you will have to remove this lamp before trying to get arcs from the secondary. The 15kV 30mA will be too much to draw through a normal 100/200W lamp. So the lamp will lightup if you try get any arcs.

The usual failure mode for a NST is one of the two output sides going short.
So you get an arc from one side to case but not the other side to case.
« Last Edit: March 21, 2019, 09:52:10 am by Psi »
Greek letter 'Psi' (not Pounds per Square Inch)
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 20357
  • Country: gb
  • 0999
Re: Is my 15KV neon light transformer broken ?
« Reply #14 on: March 21, 2019, 10:33:37 am »
This thread may be of interest. You can calculate the inductive reactance of the primary.

https://www.physicsforums.com/threads/mains-transformer-with-1-4-ohm-primary-winding.924900/

Thanks for the link.

So, my primary reactance based on my measurements above ...

Reactance :
= 2 x pi x freq x inductance
= 2 x 3.14159 x 50 Hz x 0.414 Henry
= 130.06 \$\Omega\$

So at 220 VAC the primary current will be -> 220V / 130.06 \$\Omega\$ = 1.69A ?

Much lower than the rated current (2.25A) as printed at the label isn't it ? :-//
The primary's inductance should be much higher than that. The magnetising current will be tiny, compared to when it's loaded.

The problems is the inductance of the transformer will be frequency dependant and meters often test at a much higher frequency, than the mains.

I think the transformer is most likely fine. As mentioned above, connect it to a spark gap, turn on the power and keep well back. Note that 15kV at 30mA, is a high enough voltage and current to be lethal!
 

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #15 on: March 22, 2019, 02:29:31 am »
The usual failure mode for a NST is one of the two output sides going short.
So you get an arc from one side to case but not the other side to case.

Ok, noted.

Also, the case connection from middle tap, its just for ground connection came from the mains ground line, am I right ?

Offline BravoVTopic starter

  • Super Contributor
  • ***
  • Posts: 7549
  • Country: 00
  • +++ ATH1
Re: Is my 15KV neon light transformer broken ?
« Reply #16 on: March 22, 2019, 02:31:00 am »
The primary's inductance should be much higher than that. The magnetising current will be tiny, compared to when it's loaded.

The problems is the inductance of the transformer will be frequency dependant and meters often test at a much higher frequency, than the mains.

I think the transformer is most likely fine. As mentioned above, connect it to a spark gap, turn on the power and keep well back. Note that 15kV at 30mA, is a high enough voltage and current to be lethal!

I guess I will have to try it myself, will be using variac, and still waiting for engine spark plug cable to arrive.

Offline Psi

  • Super Contributor
  • ***
  • Posts: 10385
  • Country: nz
Re: Is my 15KV neon light transformer broken ?
« Reply #17 on: March 22, 2019, 06:41:15 am »
The usual failure mode for a NST is one of the two output sides going short.
So you get an arc from one side to case but not the other side to case.

Ok, noted.

Also, the case connection from middle tap, its just for ground connection came from the mains ground line, am I right ?

Correct, HV center tap is mains earth.
The manufactures are cheap, or maybe smart, and get around some rules for insulation/isolation of high voltages by making +/- 6kV outputs instead of one 12kv output. 
A single 12kV output would require more insulation and be more expensive to make.



« Last Edit: March 22, 2019, 06:48:50 am by Psi »
Greek letter 'Psi' (not Pounds per Square Inch)
 


Share me

Digg  Facebook  SlashDot  Delicious  Technorati  Twitter  Google  Yahoo