Toroid as tested is:
core: Approximately 5.5 cm tall, 11 cm across, 6.5 cm
center hole, was best measurements I could get trying to
account for wire and insulation.
Toroid windings being used:
16 awg primary winding
16 awg secondary winding
Powered Toroid with variac set
at 120 volts out showed .01 amp current draw with no load. I thought this was kind of low.
Once powered up the Toroid out put is at 125 volts with no load then
drops to 120 @ .87amp current draw loaded with 100 watt light bulb.
I tested Volts per turn ratio and it is at 3 turns per
volts @ 120 volts input at primary.
Ok with that said, from the above testing results would this make a good isolation 120volt -120 volt transformer, good for around 3.5 amps?
It was originally a 1 kva 208-440 to 215 volt auto transformer that i removed the insulation from and separated the other sets of wires and narrowed down these two sets for my needs as an isolation transformer.
My concern is , will the windings be ok with 120 volts, or are they in reality still 220 volt windings? And if they are still 220 volt windings what problems would I notice running this on 120 volts
Also, are there any Toroid transformer calculators on line, ive searched and have not found what i was looking for.
Thanks