Author Topic: PLC analog input  (Read 2432 times)
Offline Aruck
PLC analog input
« on: June 02, 2015, 01:20:04 am »
Hi eevblog,
I've lurked for a long time, but I finally got around to making an account to ask a question. I have a basic understanding of A to D and D to A converters, sample rate, bit depth, Nyquist frequency, etc.
I'm using an Allen Bradly compact logix plc, and my plc has what's described as four "Universal Analog Input Points", each point having a terminals labeled "V in" "I in" and "V/I in".
Can someone explain to me the function of each terminal? I've tried my best to hunt through the pdf's provided by Allen Bradly but I simply can't find what I'm looking for.
Thanks in Advance.
Offline 128er
Re: PLC analog input
« Reply #1 on: June 02, 2015, 01:39:44 am »
Hi Aruck. Welcome to the forum!
First ...
Which exact model do you use? If It's a PLC with seperate CPU and I/O modules, the type of your analog input module would be good.
Dont know the allen bradley stuff exactly (more used to Siemens). But industry standard is 0-10V (sometimes 0-5V) for analog voltage inputs. And 0/4-20 mA for analog current inputs. The "V/I In" terminals are probably universal and you select the function you want to use in your PLC hardware configuration.
EDIT:
Seems that you can configure their analog input modules in every way you like. Each input independently for V or I, or even for thermocouples and RTDs
« Last Edit: June 02, 2015, 01:49:09 am by 128er »
Offline Aruck
« Reply #2 on: June 02, 2015, 02:30:44 am »
The PLC that I'm using is not a chassis / card type, everything is all built together as one unit.
You are correct about the inputs being configurable. After several hours of searching I think I found what I'm looking for. I don't understand why a voltage signal uses 2 terminals and a current signal uses 3, but I guess I'll just roll with it.
Offline Paul Moir
« Reply #3 on: June 02, 2015, 06:00:48 am »
Betcha the middle pin provides the current source for the current loop.
Online Zero999
  • 0999
« Reply #4 on: June 02, 2015, 08:42:08 am »
Can you post the full data sheet for the PLC?
Offline Rerouter
« Reply #5 on: June 02, 2015, 09:04:45 am »
measure across the middle pin and the negative for the current input, and you will likely find a 250 ohm resistor, (4mA * 250 ohm = 1 Volt, but it still needs to measure that voltage so you bridge the voltage sensing pin, and the resistor to measure current