Author Topic: PLC analog input  (Read 2859 times)

0 Members and 1 Guest are viewing this topic.

Offline AruckTopic starter

  • Contributor
  • Posts: 13
PLC analog input
« on: June 02, 2015, 01:20:04 am »
Hi eevblog,

I've lurked for a long time, but I finally got around to making an account to ask a question. I have a basic understanding of A to D and D to A converters, sample rate, bit depth, Nyquist frequency, etc.

I'm using an Allen Bradly compact logix plc, and my plc has what's described as four "Universal Analog Input Points", each point having a terminals labeled "V in" "I in" and "V/I in".

Can someone explain to me the function of each terminal? I've tried my best to hunt through the pdf's provided by Allen Bradly but I simply can't find what I'm looking for.

Thanks in Advance.
 

Offline 128er

  • Regular Contributor
  • *
  • Posts: 229
  • Country: de
Re: PLC analog input
« Reply #1 on: June 02, 2015, 01:39:44 am »
Hi Aruck. Welcome to the forum!

First ...

Which exact model do you use? If It's a PLC with seperate CPU and I/O modules, the type of your analog input module would be good.

Dont know the allen bradley stuff exactly (more used to Siemens). But industry standard is 0-10V (sometimes 0-5V) for analog voltage inputs. And 0/4-20 mA for analog current inputs. The "V/I In" terminals are probably universal and you select the function you want to use in your PLC hardware configuration.

EDIT:
Seems that you can configure their analog input modules in every way you like. Each input independently for V or I, or even for thermocouples and RTDs
« Last Edit: June 02, 2015, 01:49:09 am by 128er »
 

Offline AruckTopic starter

  • Contributor
  • Posts: 13
Re: PLC analog input
« Reply #2 on: June 02, 2015, 02:30:44 am »
The PLC that I'm using is not a chassis / card type, everything is all built together as one unit.

You are correct about the inputs being configurable. After several hours of searching I think I found what I'm looking for. I don't understand why a voltage signal uses 2 terminals and a current signal uses 3, but I guess I'll just roll with it.

 

Offline Paul Moir

  • Frequent Contributor
  • **
  • Posts: 926
  • Country: ca
Re: PLC analog input
« Reply #3 on: June 02, 2015, 06:00:48 am »
Betcha the middle pin provides the current source for the current loop.
 

Offline Zero999

  • Super Contributor
  • ***
  • Posts: 19491
  • Country: gb
  • 0999
Re: PLC analog input
« Reply #4 on: June 02, 2015, 08:42:08 am »
Can you post the full data sheet for the PLC?
 

Offline Rerouter

  • Super Contributor
  • ***
  • Posts: 4694
  • Country: au
  • Question Everything... Except This Statement
Re: PLC analog input
« Reply #5 on: June 02, 2015, 09:04:45 am »
measure across the middle pin and the negative for the current input, and you will likely find a 250 ohm resistor, (4mA * 250 ohm = 1 Volt, but it still needs to measure that voltage so you bridge the voltage sensing pin, and the resistor to measure current
 