| Electronics > Beginners |
| Random values in MegOhmmeter |
| (1/1) |
| Jasonbit:
Hello, I am trying measuring the insulation resistance of this transformer trough this MegOhmmeter (https://uk.farnell.com/tenma/72-9400/tester-insulation-250v-500v-1kv/dp/2064096). But I receive the weird values. In this images you can see three diferrent value during resistance test. The values are always changing! Image 1: https://postimg.cc/Hjy1Zyzc Image 2: https://postimg.cc/4YwD7bfM Image 3: https://postimg.cc/kVpLwJtv What could be happening? I already checked with a multimeter and got the correct voltage values (250VDC, 500VDC and 1000VDC). And the test applied to a multimeter has a value of 9.9M Ohm Thanks |
| RoGeorge:
Try measuring without the 2 spool of wires, using shorter leads (probes) instead. My best guess is those 2 spool of wires are nothing but huge coils, acting here as antennas, thus altering the measured value. |
| Andy Watson:
Can you power the meter from a battery? If not, can you ground one of the power supply leads? I suspect that your power supply is coupling a large mains component into your meg-ohm meter - which is probably saturating the front-end of the meter. And as RoGeorge points out, this will not be helped by those long antennas. |
| graeme.c.payne:
I agree with the above. As a general rule, the connection between the unit under test and the test/measurement equipment should always be as short as practical. Sent using Tapatalk |
| Jasonbit:
Thanks to your help. Yes, you are right. I did this test: image1: https://postimg.cc/7bs2xbTN image2: https://postimg.cc/LnJZhRtF When I tested the transformed in the moment I press the button "Test" the value 685MOhms appear but disappear in the next second. Then it remains with the value1 MOhm. I repeat the process and I get another value. Thanks |
| Navigation |
| Message Index |