Measure the phase current off load and on load and there won't be much difference...
No, the transformer, and motor, are constant flux devices...
How do you reconcile those 2 statements? Given how and why a constant flux machine works, namely that for the flux to remain constant the primary current must proportionally match the secondary current so that there phasor sum of the constituent magnetic fields remain constant
As an industrial electrician with 30+ years in the field, I can tell you that the current difference between no load and full load can be several orders of magnitude in difference. If this weren't the case the majority of overload protection devices would not work as they monitor current amplitude only. The older types relied on the heating effect of a given current (I^2R nothing else), the newer ones model that same heating effect in software
It's cooling which limits how much power a motor can safely output. If the motor is specified at an ambient temperature of 30oC, then it should be able to output more power at 10oC. There's a limit on how low the temperature can go of course: too cold and the grease in the bearings will solidify, causing more friction and higher power dissipation.
I actually think that there is more to the power rating of a motor than just the cooling. Let's say that I could put infinite cooling onto the motor while operating it. Then I would say that a big motor will be stronger than a small one. Of course, if the bigger motor is poorly designed, then this won't apply. I guess that internal resistance plays a role here. So either internal resistance or maximum torque @ a given RMS voltage level would give what's missing in the equation. I guess.
What limits the power rating is the maximum temperature rating of the motor windings. At lower temperatures, the windings will be able to dissipate more energy before overheating. Another thing is the resistance of copper and other metals is lower at lower temperatures, so the power dissipation will also fall, given the same load (the efficiency will increase): running at lower temperatures is a win-win.
Assuming we are talking about the power a motor can output and not just the power it consumes, then mechanical constraints come into play as well such as shaft sizes, the bearings, construction of the rotor bars. A common failing is cracked rotor bars due to mechanical over loading and shock loading. Electrically, iron core saturation comes into play as well
I don't understand this. If something happened to one of the windings so that it draws more current/power than the other windings, for one reason or another. Then why should that lead to any significant voltage drop? I'm talking about voltage between the phases here. If I measured the voltage over a 2kW heater and then a 20W light bulb, there wouldn't be any significant voltage difference. Amperage difference yes, voltage difference no. Not if the cabling is good anyway.
If the currents are imbalanced for what ever reason, imaging the following.
The rotating magnetic field can be represented by a vector with an origin fixed at zero, spinning around in some direction with a fixed amplitude if all phase currents are balanced.
If we take into account only one phase current and look at what that produces as a magnetic field it would be stationary and its amplitude would grow, diminish, changed direction, grow, diminish, following the currents sinusoidal amplitude. If we take all three phases' magnetic fields and sum them we get our original spinning vector.
This is easier to visualise if you take just 2 phases 90 degrees out of phase with each of their poles physically displaced by 90 degrees also.
Back to our original scenario with one phase having different current. Aside from now having an imbalanced 3 phase system with phase currents all over the place the magnetic field created by these currents is no longer of fixed amplitude and spinning in a nice synchronous manner. This causes the motor to sound angry as the rotor hunts and slips all over the place as it locks and unlocks from the now ruined rotating magnetic field.