| Gregg:
A word of caution using CTs: don’t leave them open circuit with a load. Because of the high turns ratio, the voltage can become very high and degrade the insulation between turns, ruin test equipment and give you a nasty shock. Industrial installations of CTs often include a junction block with shorting bars positioned so that the CTs can be shorted before removing the metering devices. |
| Zero999:
Why not get another current transformer and run it in reverse? You can then get 10A out from a much lower current supplied by the variac, with a small 6V transformer on the secondary. |