I am after variable frequency drive, to control the electric motor RPM via RS485(Modbus).
There is a Bosch Rexroth EFC5610 VFD, which I really like, it has an in-build motor thermal protection, but in Modbus communication description it warns that the registers read/write limit is only 150000 times/register. I will be changing the frequency registers frequently and that worries me.
I had a look at other VFDs (Siemens V20, Schneider ATV12, Parker AC10) and none of their manuals mention the Modbus communication limits for read/write cycles per register.
A lot of the industrial electronics seem to have unwritten defaults and I wonder whether the 150k cycles mentioned by Bosch is default for majority of VFDs, or is it just the big drawback of the EFC5610 VFD?
Thanks
Offline Kalin
I have never hear of that with other drives and never run into a failure to write to memory with any drives I have used even the ones that use an eeprom for storing parameters. How often do you plan on writing to this value?
Sent from my SM-G965W using Tapatalk
... How often do you plan on writing to this value?
The motor is for a small test rig, to test parts. The test would use up to 10 different frequencies (not pre-set ones). The test could be run to to ten times an hour, 8 hours a day.  So pretty much in theory, the registers would be shot within a year :(
I would have thought the read/write count would be much greater, considering todays interconnected controls in the industrial environment.
Offline Kalin
Would you consider another manufacturer or have you already purchased the drives? It might be a typo because that is not really an acceptable number for any application I can imagine for a VFD.
I was not far from placing the order, luckily found the info in time. I just wanted to make sure it does not apply universally throughout VFDs before considering different manufacturer.
I do not think it is a typo, because the read/write limit is throughout a number of revisions I checked and they have warning in a number of manual sections.