Author Topic: What is isolation level of isolated DCDC module?  (Read 1897 times)

0 Members and 1 Guest are viewing this topic.

Offline ocsetTopic starter

  • Super Contributor
  • ***
  • Posts: 1516
  • Country: 00
What is isolation level of isolated DCDC module?
« on: February 25, 2018, 11:05:37 am »
Hello,
 We need an isolated DCDC module to give 15V output from a 13V input. Its to provide isolated power to a DALI comms bus from a non mains isolated source.
We need full mains isolation. This is usually described as being able to withstand a hi-pot test at “3000VAC at 50Hz for one second”.

However, the Traco TEN 3-1213  DCDC module   states  isolation of “1500VDC for one second”.

Do you think that this is therefore safe to use for our DALI comms bus? (ie, does it equate to full mains isolation)?  :-//

Traco TEN 3-1213 DCDC module   datasheet
http://www.farnell.com/datasheets/2200535.pdf?_ga=2.114611086.845751712.1519485949-287702491.1506211291
 8)
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 7817
  • Country: de
  • A qualified hobbyist ;)
Re: What is isolation level of isolated DCDC module?
« Reply #1 on: February 25, 2018, 12:21:33 pm »
If you need an isolation withstanding at least 3kV AC the Traco is the wrong DC-DC converter. It could be just a ferrite toroid with some magnet wire only relying on the enamel coating. For mains isolation there should be also insulating tape between the windings.
 
 
The following users thanked this post: ocset

Offline ogden

  • Super Contributor
  • ***
  • Posts: 3731
  • Country: lv
Re: What is isolation level of isolated DCDC module?
« Reply #2 on: February 25, 2018, 12:22:22 pm »
Do you think that this is therefore safe to use for our DALI comms bus? (ie, does it equate to full mains isolation)?  :-//

Standards does not say "full mains isolation", they are much more specific. You shall not rely your safety-related design decisions on public forum knowledge where anyone can say anything.

If it is required to withstand a hi-pot test at “3000VAC at 50Hz for one second”, then isolation of “1500VDC for one second” does not meet the specs no matter how you are trying to twist it or look at it.

You shall either change specs of your product and state it's isolation as “1500VDC for one second” or just meet what's required by DALI or whatever document you are referring to regarding 3000VAC.
 
The following users thanked this post: ocset

Offline Ian.M

  • Super Contributor
  • ***
  • Posts: 12885
Re: What is isolation level of isolated DCDC module?
« Reply #3 on: February 25, 2018, 12:38:54 pm »
3000V RMS is 4243V peak.   You therefore need a module with a 5KV DC isolation rating *BUT* as your design requirements call for 3KV AC RMS rating, you should check with the module  manufacturer that its suitable unless it also has an AC rating >=3KV.
 
The following users thanked this post: ocset

Offline ocsetTopic starter

  • Super Contributor
  • ***
  • Posts: 1516
  • Country: 00
Re: What is isolation level of isolated DCDC module?
« Reply #4 on: February 25, 2018, 01:16:48 pm »
Thanks, we need the type of isolation that you get from primary to secondary in an offline isolated power supply for eg a domestic product....where human hands might touch the output. "basic" insulation level.

The alternative NXJ1S1215 has 4.2kV of isolation. 3000VAC * sqrt(2) is 4240Vpk
Maybe that just scrapes inside  the regs?
So i reckon the 4.2kvDC of isolation should give us  "basic"  insulation level?

NXJ1S1215
http://www.farnell.com/datasheets/2282933.pdf?_ga=2.13815998.845751712.1519485949-287702491.1506211291
« Last Edit: February 26, 2018, 06:11:25 am by treez »
 

Offline daveshah

  • Supporter
  • ****
  • Posts: 356
  • Country: at
    • Projects
Re: What is isolation level of isolated DCDC module?
« Reply #5 on: February 25, 2018, 01:24:28 pm »
According to the datasheet for that part, it says "The NXJ1 series has been recognised by Underwriters Laboratory (UL) to UL 60950 for reinforced insulation to a working voltage of 200Vrms and for basic insulation to a working voltage of 250Vrms." - so it would be OK for basic insulation for UK mains (unless you're in a part of the UK with 290V mains :popcorn:)
 
The following users thanked this post: SeanB, ocset

Offline max_torque

  • Super Contributor
  • ***
  • Posts: 1303
  • Country: gb
    • bitdynamics
Re: What is isolation level of isolated DCDC module?
« Reply #6 on: February 25, 2018, 02:03:35 pm »
But you are driving that DCDC with a 13v supply? so presumably already have some HV isolation upstream?

If you have say a fixed transformer, then the HV winding is wound onto the same physical location as the secondary, and so high levels of isolation voltage are sensible, but driving an isolated LV module, hmm im not so sure?  (because it would take multiple failures to cause a breakdown)

But, it's your product, you need to evaluate the risk / hazard and set appropriate levels, and provide suitable matching engineering solutiions
 
The following users thanked this post: ocset

Offline ocsetTopic starter

  • Super Contributor
  • ***
  • Posts: 1516
  • Country: 00
Re: What is isolation level of isolated DCDC module?
« Reply #7 on: February 25, 2018, 02:31:59 pm »
Quote
But you are driving that DCDC with a 13v supply? so presumably already have some HV isolation upstream?
Thanks, the 13V supply is non isolated from the mains.
It comes from a High voltage,  non isolated  buck converter called LNK304. (from power.com)
 

Offline T3sl4co1l

  • Super Contributor
  • ***
  • Posts: 21753
  • Country: us
  • Expert, Analog Electronics, PCB Layout, EMC
    • Seven Transistor Labs
Re: What is isolation level of isolated DCDC module?
« Reply #8 on: February 25, 2018, 02:37:26 pm »
Basic insulation means the secondary side must be grounded.

Tim
Seven Transistor Labs, LLC
Electronic design, from concept to prototype.
Bringing a project to life?  Send me a message!
 
The following users thanked this post: ocset

Offline ocsetTopic starter

  • Super Contributor
  • ***
  • Posts: 1516
  • Country: 00
Re: What is isolation level of isolated DCDC module?
« Reply #9 on: February 25, 2018, 04:20:31 pm »
Thanks, in fact, ive dug out a DALI spec which says

Quote
The minimum requirement for system components conformant to this standard shall be basic
insulation as defined in IEC 61347-1.
But we dont have IEC61347-1 and it costs £120.
 

Offline max_torque

  • Super Contributor
  • ***
  • Posts: 1303
  • Country: gb
    • bitdynamics
Re: What is isolation level of isolated DCDC module?
« Reply #10 on: February 25, 2018, 05:36:39 pm »

Thanks, the 13V supply is non isolated from the mains.


Under what failure modes can that 13v output exceed 50vdc?  As it isn't "Normally" at HV, then you don't need downstream isolation (unless you have other reasons to do so, for example, for galvanic isolation to AC supply E / N etc)

A large clamping diode on the output of the 13v supply (at say 22v), and a fuseable link  that blows, would result in the system failing "safe" in the case of a single failure. In that case, the HV applied to the DC:DC is only "short term" rather than continuous, which changes the safety case.

How many "cascade" failures are you going to design to prevent?
 
The following users thanked this post: ocset

Offline T3sl4co1l

  • Super Contributor
  • ***
  • Posts: 21753
  • Country: us
  • Expert, Analog Electronics, PCB Layout, EMC
    • Seven Transistor Labs
Re: What is isolation level of isolated DCDC module?
« Reply #11 on: February 26, 2018, 12:24:11 am »
Under what failure modes can that 13v output exceed 50vdc?  As it isn't "Normally" at HV

Not mains isolated --> mains referenced --> probably has 240VAC, -160VDC on it, plus infrequent 2.5kV+ common mode surges.

Basic insulation is required if the secondary side is grounded, otherwise Reinforced insulation is required.

Tim
Seven Transistor Labs, LLC
Electronic design, from concept to prototype.
Bringing a project to life?  Send me a message!
 
The following users thanked this post: ocset

Offline ocsetTopic starter

  • Super Contributor
  • ***
  • Posts: 1516
  • Country: 00
Re: What is isolation level of isolated DCDC module?
« Reply #12 on: February 26, 2018, 06:09:14 am »
Thanks, do you think that the 4.2kVDC of insulation in the NXJ1S1215 DCDC module conforms to "reinforced insulation"?

NXJ1S1215
http://www.farnell.com/datasheets/2282933.pdf?_ga=2.13815998.845751712.1519485949-287702491.1506211291
« Last Edit: February 26, 2018, 06:11:08 am by treez »
 

Offline T3sl4co1l

  • Super Contributor
  • ***
  • Posts: 21753
  • Country: us
  • Expert, Analog Electronics, PCB Layout, EMC
    • Seven Transistor Labs
Re: What is isolation level of isolated DCDC module?
« Reply #13 on: February 26, 2018, 07:33:39 am »
Thanks, do you think that the 4.2kVDC of insulation in the NXJ1S1215 DCDC module conforms to "reinforced insulation"?

Dude, you already thanked the post that has your answer:

According to the datasheet for that part, it says "The NXJ1 series has been recognised by Underwriters Laboratory (UL) to UL 60950 for reinforced insulation to a working voltage of 200Vrms and for basic insulation to a working voltage of 250Vrms." - so it would be OK for basic insulation for UK mains (unless you're in a part of the UK with 290V mains :popcorn:)

Also, 290V, nice catch daveshah :-DD

Tim
Seven Transistor Labs, LLC
Electronic design, from concept to prototype.
Bringing a project to life?  Send me a message!
 
The following users thanked this post: ocset