the short circuit current of the mains can be as high as 2000A in the worst cases
Not according to the IEC standards. There is a reason they rate the fault currents on safety fuses much higher.
What number do they say it is?
How long is a piece of string?
Icu is the figure that is quoted on devices for safe breaking protection. Whatever the instantaneous fault current it has to be interrupted
SAFELY.
Check out the local regulations, however a clue to that question is the breaking capacity rating printed on your MCB or RCD etc.,
6 - 10kA is normal for a final circuit in a domestic property in the UK. Some large MCCB are commonly available to safely interrupt 200kA.
One poster here put "in defence of the newbie". The fact is in these circumstances when things go horribly wrong because of abject arrogance and ignorance you don't have to defend the newbie because they are dead.
If people are willing to piss around with high energy circuits without even READING THE MANUAL for the test instrument they are trying to use, they are then nominating themselves for a Darwin award.
There are good "electricians" meters available that have no current range on them at all, any in service current measurements of high energy circuits, should for safety be made with non contact methods.
Remember RTFM