I want to order some magnet wire (they are very thinly insulated which afaik warrant caution) for a 12V/9V hobby project to be connected to my electricity grid (230V), but seeing at Wikipedia that AWG 30 is apparently rated as "338.6 milli ohm /m" and the AWG 24 as "84.22 milli ohm/m", I can't help but wonder if there is some obvious preferred choice here between AWG 30 and AWG 24.
So I am wondering, is there a preferred choice in relation to the rated resistance between AWG 30 and AWG 24? Asthis isn't something obvious to me other than having less resistance in a component for electronics sounds good as a general trait. Also assuming here that we are happy with the rated "fuse current". (seen in the table linked below)
https://en.wikipedia.org/wiki/American_wire_gauge#Tables_of_AWG_wire_sizes
I am also unsure how to interpret the "fuse current" data, which has three columns for ~10s, 1s and 32ms. Seems to me that this indicates how many seconds the wire with different wire gauges will remain intact before burning up. Am I correct in assuming that "~10s" is to mean an indefinitely long time?
Beginner to beginner.
The milliOhm per meter multiplied by the number of meters will give you a resistance value for the length of wire you are using. Ohm's law will then give you the voltage drop across that, for a given current. Lets say you want to run 1Amp.
Example:
338.6 milli ohm /m * 5 meters = 1.7 Ohm.
V=IR
V=1.7Ohm * 1 Amp
V=1.7V drop
Now we have the voltage drop and the current we can work out the amount of power lost in the wire as heat.
1.7V * 1A = 1.7W
Not an awful lot of heat in a 5 meter bit of wire, but 1.7V is a significant lose that could cause your circuit to fail.
Obviously if you are using shorted runs there will be less voltage drop and less heat.
Be careful with wire gauge tables and charts on line, they are often "Chassis", "Automotive" or "Main standard" ratings. If you have a wire running 20 meters through a house that is meant to handle 30A and last for 50 years without getting hot it will have to be a much more sizable conductor than a 10cm lead across a desk in a hobby project which is only used for short periods under supervision. In RC Model flying we would typically drop a couple of wire sizes as we can accept a bit of heat at burst currents and the models are usually only running for 10-20mins at time.
(Running 100A through 12 or 14 gauge wire would have an electrical installation engineer in tears of fear, but it's fine for short bursts over a 6 inch cable).
The fuse rating with time is, I believe, as you suggest, the amount of time the wire will sustain before it burns through.
"~" normally means approximately. So ~10s means approximately or "circa" 10 seconds.