Wire testing, OK or not
« on: September 24, 2019, 10:42:13 pm »
A friend of mine who is an electrician told me that he tests all circuits with high voltage of 10kV.
He does that to check if the wire was nicked or somehow damaged during construction before they start closing the walls.
A typical Romex 12-14AWG wire used for wiring the house has insulation voltage rating of 600V. Is it OK to stress the insulation on the wire with 10kV?
 

Offline ataradov

  • Super Contributor
  • ***
  • Posts: 11905
  • Country: us
    • Personal site
Re: Wire testing, OK or not
« Reply #1 on: September 24, 2019, 11:06:39 pm »
It is fine, but probably pointless. What exactly are they looking for in that test? And what is the source of that 10 kV voltage?
Alex
 

Offline IvoSTopic starter

  • Frequent Contributor
  • **
  • Posts: 312
  • Country: us
Re: Wire testing, OK or not
« Reply #2 on: September 24, 2019, 11:16:43 pm »
primarily looking for insulation integrity, if the wire was cut or the insulation is somehow compromised
 

Offline ataradov

  • Super Contributor
  • ***
  • Posts: 11905
  • Country: us
    • Personal site
Re: Wire testing, OK or not
« Reply #3 on: September 24, 2019, 11:18:47 pm »
Yes, but what is observed/expected when the voltage is applied? Do they apply high voltage and run around looking for discharge/sparks?
Alex
 

Offline ataradov

  • Super Contributor
  • ***
  • Posts: 11905
  • Country: us
    • Personal site
Re: Wire testing, OK or not
« Reply #4 on: September 24, 2019, 11:24:38 pm »
This also assumes that there is only wiring and no other devices including RCDs and may be even light switches. Otherwise you are just asking for trouble.
Alex
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8135
  • Country: gb
Re: Wire testing, OK or not
« Reply #5 on: September 24, 2019, 11:43:06 pm »
10kV is nonsense.

1kV and below, yes, insulation resistance testing is normal. Well, in some places..
 

Offline vk6zgo

  • Super Contributor
  • ***
  • Posts: 7858
  • Country: au
Re: Wire testing, OK or not
« Reply #6 on: September 25, 2019, 12:32:17 am »
Maybe some "Meggers" can produce 10kV, although the highest I've seen is 1kV.

Years ago,we had a thing  called a "Trimax Ionisation Tester" at several of my employers.
From memory, it could test at up to about 25kV, but like a Megger, it couldn't produce dangerous or damaging current levels.

Perhaps something similar?
 

Offline tkamiya

  • Super Contributor
  • ***
  • Posts: 2178
  • Country: us
Re: Wire testing, OK or not
« Reply #7 on: September 25, 2019, 01:00:10 am »
I was professionally trained as electrician in Japan.

Back then, Megger was a hand crank type.  They easily put out few KV but very little current.  Even if there is a huge nick and short, current was so low, it did not cause any (additional) damage.  Cable damage can happen by accident (putting nail through, scrapes, or rats chewing on insulation).  Megger will let you know the cable has leak.  Again, current was low enough that it didn't cause any damage.

Of course, if you have any electronics plugged in, it would be advisable to unplug them.
 

Offline MosherIV

  • Super Contributor
  • ***
  • Posts: 1530
  • Country: gb
Re: Wire testing, OK or not
« Reply #8 on: September 25, 2019, 06:44:09 am »
Hi

We have an insulation tester called a Voltage Withstand Tester at work. It tests up to 6KV.

Technically, you only need to run a voltage withstand test once on a product to proove/validate a new product's specifications.

Does it damage the insulation?
Depends on the nature of the insulation breakdown.
If the breakdown results in an arc that leaves behind conductive resdue then, yes the insulation has been compromised and damaged.
It is possible to have a breakdown where the hv finds a leakage path and does little/no damage.

Each time you run a voltage withstand test, it does stress the insulation.
 