| martincho:
I have to test a design with an input voltage range reaching at least 400 VAC and possibly 480 VAC. Power consumption is about 250 W, so not a lot of current. Trying to figure out the most economical way to get there. My first thought was to get a step-up variac (variable transformer) that can run off 240 VAC and get to at least 400. They do exist. Cost is about $2,000, which is fine. Any other reasonable options? Even used lab equipment would be fine. I just don't have any part numbers to run a search. For example, did companies like HP or Tektronix make such high voltage variable output voltage power supplies? While I have 240 VAC single phase, I also have a digital phase converter putting out 3 phase for a CNC milling machine. When I installed it I also installed a 4-prong twist-lock on the wall for any future application that could use this power. I wonder if this might be the ticket? Can I use two phases and get legit 480-is out of it? I haven't thought this one through yet. The device being powered is a switch-mode power supply rated for something like 300 to 500 VAC input. Thanks, -Martin |
| bdunham7:
The obvious way would simply be a 1:2 or 1:4 step-up transformer, with a variac in front of it if you like. https://www.powervolt.com/group-ag-input-240-480vouput-120-240vpower-25-to-1500va-pd-164 |
| NiHaoMike:
Perhaps get a transformer designed to provide 120V or 240V from 480V and use it backwards? Might also work to use a microwave oven transformer (or two with secondaries in parallel and primaries in series) on a variac, add an end stop on the variac to prevent turning it up too much by mistake. It would also work for supplying 600V if there's a need later on. |
| jmelson:
"Step down transformers" were used in a lot of industrial equipment to run computers and general items from the shop floor 480 V mains. These have jumpers to select the input and output range. They can be connected in reverse to step up the voltage. So, set jumpers for 480 to 240 V configuration, and then feed 240 to the LV side and get 480 from the HV side. You can get one of these at a scrapyard for the metal scrap value. Then, use a standard 240 V Variac to feed it. Jon |
| Ground_Loop:
I have a 4 KVA 480-120 transformer running backward as a supply to several VFDs in my shop. I've been using it for more than 20 years without issue. |