Electric Use/bill excessive?
« on: September 16, 2016, 05:19:16 pm »
Landlord quoted electric bill 1/2 of experienced useage. Entering 16th month of service from Dominion Power. 2-bedroom apt. has multiple receptacles wired improperly--as tested by plug-in wiring testers.

I've noted LED bulbs glowing when turned "Off". What is happening? What about other receptacles with electronics plugged in/turned "Off"?

Question: Are improperly-wired receptacles consuming occult power continuously--thus running up the electricity useage?

linr05 @ground level

 

Offline Ampera

  • Super Contributor
  • ***
  • Posts: 2578
  • Country: us
    • Ampera's Forums
Re: Electric Use/bill excessive?
« Reply #1 on: September 16, 2016, 05:52:17 pm »
Landlord quoted electric bill 1/2 of experienced useage. Entering 16th month of service from Dominion Power. 2-bedroom apt. has multiple receptacles wired improperly--as tested by plug-in wiring testers.

I've noted LED bulbs glowing when turned "Off". What is happening? What about other receptacles with electronics plugged in/turned "Off"?

Question: Are improperly-wired receptacles consuming occult power continuously--thus running up the electricity useage?

linr05 @ground level

No. Unless there is something in your plug that can draw current (There isn't) then there is no possible way you will be losing energy through the plug. And when you think about the law stating energy never disappears, rather it changes form, means if you were losing current through an outlet, you would see or feel something.

If your sockets aren't wired properly, simply A. Know what you are doing, or get someone who does, and B. You can unscrew them and rewire them (MCBs off please) proper.

My guess for the LED Bulbs is maybe a cap discharging or something. LED bulbs tend to have mini PSUs in them, which could use caps for power filtering, thus when you turn the bulb off it might glow dimly for a few minutes afterwards. Try unplugging it to see if my theory is correct.

Also your English (I understand not trying to offend here) isn't the greatest, but if you mean to say that your landlord said you only used 1/2 of the expected power usage, where is the problem?
I forget who I am sometimes, but then I remember that it's probably not worth remembering.
EEVBlog IRC Admin - Join us on irc.austnet.org #eevblog
 

Offline System Error Message

  • Frequent Contributor
  • **
  • Posts: 473
  • Country: gb
Re: Electric Use/bill excessive?
« Reply #2 on: September 16, 2016, 09:19:22 pm »
Use a wattmeter to check what consumes power. Perhaps some PSU is consuming a lot of power. Perhaps an electrical short is consuming power. Measure every device and add them up and compare to your meter the rate at which it is running it. If the calculation is close it is fine and you are just using a lot of power. Otherwise there could be something you didnt measure using electricity.
 

Offline fubar.gr

  • Supporter
  • ****
  • Posts: 369
  • Country: gr
    • Fubar.gr
Re: Electric Use/bill excessive?
« Reply #3 on: September 16, 2016, 10:14:06 pm »
Light switches that have a neon indicator (so you can find them at night) constantly pass a tiny amount of current for the neon bulb. This current can be enough to make LEDs on the same circuit glow very dimmly.

This current is so small that it would amount to just a few pennies per year on the power bill.

Some times LEDs glow because they are picking up energy from capacitive coupling with adjacent wires. Again the power lost is so tiny that shouldn't be of concern.

Offline Whales

  • Super Contributor
  • ***
  • Posts: 2091
  • Country: au
    • Halestrom
Re: Electric Use/bill excessive?
« Reply #4 on: September 16, 2016, 11:41:25 pm »
Use a wattmeter to check what consumes power. Perhaps some PSU is consuming a lot of power. Perhaps an electrical short is consuming power. Measure every device and add them up and compare to your meter the rate at which it is running it. If the calculation is close it is fine and you are just using a lot of power. Otherwise there could be something you didnt measure using electricity.

If a short exists then it will be drawing a lot of power.  Imagine the heating effects of a multi-thousand watt heater. 

If you think your house wiring is incorrect or dangerous, then the best line of action is to get an electrician to look at it.

Offline Ampera

  • Super Contributor
  • ***
  • Posts: 2578
  • Country: us
    • Ampera's Forums
Re: Electric Use/bill excessive?
« Reply #5 on: September 17, 2016, 12:53:11 am »
Maybe one of your neighbors is tapping into your line. Could just be gremlins too.

Can't tell you how many times I've had to deal with mains gremlins. I saw some once on a trip to Germany, they are a damn sight more vicious than ours in America.
I forget who I am sometimes, but then I remember that it's probably not worth remembering.
EEVBlog IRC Admin - Join us on irc.austnet.org #eevblog
 

Offline retrolefty

  • Super Contributor
  • ***
  • Posts: 1648
  • Country: us
  • measurement changes behavior
Re: Electric Use/bill excessive?
« Reply #6 on: September 17, 2016, 01:57:38 am »
Quote
Some times LEDs glow because they are picking up energy from capacitive coupling with adjacent wires. Again the power lost is so tiny that shouldn't be of concern.

 Glowing? I find that a little unlikely, do you have a model circuit to show such behaviour?

 

Offline timb

  • Super Contributor
  • ***
  • Posts: 2536
  • Country: us
  • Pretentiously Posting Polysyllabic Prose
    • timb.us
Re: Electric Use/bill excessive?
« Reply #7 on: September 17, 2016, 02:13:49 am »
Quote
Some times LEDs glow because they are picking up energy from capacitive coupling with adjacent wires. Again the power lost is so tiny that shouldn't be of concern.

 Glowing? I find that a little unlikely, do you have a model circuit to show such behaviour?

I've seen it on LED bulbs as well. It's a very, very, very feint glow that you can only really see in a dark room once your eyes adjust. Maybe the coating on the inside of the bulb has some sort of phosphorescent effect? Maybe it's just a very small residual charge from the main decoupling cap, or even sub-microamp leakage from a Y cap causing the LED to glow? (LEDs can be visible in a dark room with just 1uA of current.)
Any sufficiently advanced technology is indistinguishable from magic; e.g., Cheez Whiz, Hot Dogs and RF.
 

Offline StillTrying

  • Super Contributor
  • ***
  • Posts: 2850
  • Country: se
  • Country: Broken Britain
Re: Electric Use/bill excessive?
« Reply #8 on: September 17, 2016, 02:16:19 am »
I've seen very low power CFL sometimes glow or flash when off when they're on an electronic time switch or dimmer, but not LEDs, are these LEDs CFLs.

.  That took much longer than I thought it would.
 

Offline dannyf

  • Super Contributor
  • ***
  • Posts: 8221
  • Country: 00
Re: Electric Use/bill excessive?
« Reply #9 on: September 17, 2016, 02:18:06 am »
Quote
Landlord quoted electric bill 1/2 of experienced useage.

why don't you ask to see the bill? they cannot fudge the readings over a long period of time.
================================
https://dannyelectronics.wordpress.com/
 

Offline Someone

  • Super Contributor
  • ***
  • Posts: 5098
  • Country: au
    • send complaints here
Re: Electric Use/bill excessive?
« Reply #10 on: September 17, 2016, 07:36:06 am »
Quote
Some times LEDs glow because they are picking up energy from capacitive coupling with adjacent wires. Again the power lost is so tiny that shouldn't be of concern.

 Glowing? I find that a little unlikely, do you have a model circuit to show such behaviour?

I've seen it on LED bulbs as well. It's a very, very, very feint glow that you can only really see in a dark room once your eyes adjust. Maybe the coating on the inside of the bulb has some sort of phosphorescent effect? Maybe it's just a very small residual charge from the main decoupling cap, or even sub-microamp leakage from a Y cap causing the LED to glow? (LEDs can be visible in a dark room with just 1uA of current.)
It can be seen in in fluorescent tubes too, when the room is very dark and you have some dark adaption there is some residual glow long after the excitation has been removed. I'm not sure if its just a long fluorescence lifetime combined with the extreme flux of the tube or if there is some phosphorescent component.
 

Offline tatus1969

  • Super Contributor
  • ***
  • Posts: 1273
  • Country: de
  • Resistance is futile - We Are The Watt.
    • keenlab
Re: Electric Use/bill excessive?
« Reply #11 on: September 17, 2016, 07:44:01 am »
Maybe one of your neighbors is tapping into your line. Could just be gremlins too.

Can't tell you how many times I've had to deal with mains gremlins. I saw some once on a trip to Germany, they are a damn sight more vicious than ours in America.
Yeah I know, we always have the good stuff. Made in Germany.

P.s. "Made" is also a German word meaning grub.
We Are The Watt - Resistance Is Futile!
 

Online BradC

  • Super Contributor
  • ***
  • Posts: 2123
  • Country: au
Re: Electric Use/bill excessive?
« Reply #12 on: September 17, 2016, 07:48:28 am »
With capacitive coupling CFLs flicker and LEDs glow.

In both cases the coupling slowly (relatively, this can happen multiple times a second if it's strong enough) charges up the bulk storage electro in the SMPS. When the voltage gets high enough the lamp tries to start causing a pulse of light. On the CFL you see that as a dim flicker, but on a LED bulb there is a much higher density phosphor coating that effectively low-pass filters the emission from the led and you get a very dim glow from that.

Don't mistake that from the turn-off glow. LED bulbs can take minutes for the glow to completely decay after a switch off. CFLs do too, but the decay is generally a *lot* quicker.
 

Offline SteveyG

  • Supporter
  • ****
  • Posts: 997
  • Country: gb
  • Soldering Equipment Guru
Re: Electric Use/bill excessive?
« Reply #13 on: September 17, 2016, 08:31:51 am »
Quote
Some times LEDs glow because they are picking up energy from capacitive coupling with adjacent wires. Again the power lost is so tiny that shouldn't be of concern.

 Glowing? I find that a little unlikely, do you have a model circuit to show such behaviour?

It's very common, particularly on 2 way wiring where the strappers are next to each other in the 3C+E wires. It's also likely to happen where you've lost your earth on the twin and earth cable going to the switch.
YouTube Channel: https://www.youtube.com/user/sdgelectronics/
Use code: “SDG5” to get 5% off JBC Equipment at Kaisertech
 

Offline linr05Topic starter

  • Newbie
  • Posts: 2
Re: Electric Use/bill excessive?
« Reply #14 on: September 19, 2016, 01:33:53 am »
With capacitive coupling CFLs flicker and LEDs glow.

In both cases the coupling slowly (relatively, this can happen multiple times a second if it's strong enough) charges up the bulk storage electro in the SMPS. When the voltage gets high enough the lamp tries to start causing a pulse of light. On the CFL you see that as a dim flicker, but on a LED bulb there is a much higher density phosphor coating that effectively low-pass filters the emission from the led and you get a very dim glow from that.

Don't mistake that from the turn-off glow. LED bulbs can take minutes for the glow to completely decay after a switch off. CFLs do too, but the decay is generally a *lot* quicker.
Thx 4 this info. Other inputs: I guess I'm just a power glutton compared to the old occupants. End of post/quandary.