SeanB,
With the recent changes to SANS10142 (ADMT

, you can have a loophole on Insulation Resistance tests , just get the customer to plug a Computer or Medical Device into the socket, then make use of the following loophole :
Insulation Resistance Testing:
NOTE 2 In the case of existing installations where the power may not be switched
off from certain circuits in order to carry out this test, the fact that the circuits are
subject to the supply voltage can be regarded as evident that the insulation
resistance is compliant. Amdt 8
----
But to anybody that wants to exploit a loophole like this, remember, it is your a*se if you pass the compliance, and a fire breaks out, or if somebody gets killed because you took a shortcut. And anyway, if you do the proper testing :
1) You can be sure that the Insulation Resistance is good, or
2) You have a business oppertunity to make money replacing the cables
and it will be passed so long as the wiring still meets minimum insulation levels ( good luck doing that with 50 year old DCC wire though, there you will rewire in all probability)