Author Topic: high qualtiy lightning rod  (Read 1134 times)
Online coppercone2Topic starter
« on: April 06, 2024, 09:18:45 am »
They don't build them like they used to. Manufacturers are always making conductors thinner nowadays.
https://www.accuweather.com/en/weather-news/a-bolt-of-lightning-strikes-the-statue-of-libertys-torch/1638224
Offline tooki
Re: high qualtiy lightning rod
« Reply #1 on: April 06, 2024, 10:33:49 am »
And what’s the evidence for this? Or is this just another of your fever-dream “the olden days were always better” conspiracy theories pulled out of thin air?
The physics of lightning haven’t changed, and the thickness of the lightning protection conductors is prescribed by code. That’s NFPA 780 for you in USA. Tables 4.1.1.1.1 and 4.1.1.1.2 on page 780-11 (PDF page 14) of the standard, attached below, give the required conductor cross-sections for both copper and aluminum conductors.
Online Gyro
« Reply #2 on: April 06, 2024, 10:51:26 am »
According to my between the wars 'Wonders of World Engineering' book. The copper shell (approx 3/32" thick) was insulated from the iron frame by Shellac coating and Asbestos strips so that no part was in direct contact, to prevent electrolytic corrosion. Obviously it wouldn't eradicate direct corrosion of the Iron from salt, but it helped it survive for well over 100 years before replacement.
Edit: I would assume that most of the lightning discharge current probably passes to ground via the copper shell, it would be difficult to sufficiently insulate a lightning conductor at the top.
« Last Edit: April 06, 2024, 11:26:55 am by Gyro »
Best Regards, Chris
Offline ebastler
« Reply #3 on: April 06, 2024, 03:42:37 pm »
I took coppercone's post as a humorous one. The whole Statue of Liberty acting as a lightning rod, with undoubtedly larger cross-section than what you would typically find today (or yesterday, for that matter...) 8)
The following users thanked this post: NiHaoMike, nctnico
Online Zero999
  • 0999
« Reply #4 on: April 07, 2024, 09:01:15 am »
Exactly. I seriously doubt a structure made of iron and copper needs a lightning conductor.
Offline jonpaul
    • IEEE Spectrum
« Reply #5 on: April 07, 2024, 11:00:57 am »
In USA nowadays, the wiring, earthing, bonding and rods are well specified in the regulatory, NEC, NFPA, etc.
I am sure other locales EU, AU, UK have smilar.
I have not  encountered anything but thick copper rods, clamps, wiring.
Earthing is usueally a number of 0.375" = 8mm 10' long copper rods spaced out in moist earth.
Resistance to the earth is specified and measured.
Bon Chance
Jon
An Internet Dinosaur...
Offline tooki
« Reply #6 on: April 07, 2024, 11:14:20 am »
Well, it does need one to bridge the base, since the copper is not in the soil.
I also wonder whether the infernal iron structure is grounded separately, since it is insulated from the copper to prevent galvanic corrosion.
Online Zero999
  • 0999
« Reply #7 on: April 07, 2024, 11:21:34 am »
I would have thought there would be some sort of electrical connection to limit the voltage between the two, yet also limit corrosion. Sacrificial anodes connected to earth, or a spark gap, which limits the voltage below 1kV, so it doesn't damage the insulation, when lighting strikes.
Offline tooki
« Reply #8 on: April 07, 2024, 11:30:14 am »
Could be, I don’t know the details. (Haven’t looked into it. I just know I found mention of them being insulated to prevent corrosion.)
Offline shapirus
  • Country: ua
« Reply #9 on: April 07, 2024, 11:41:07 am »
I too have always had a feeling that there was a slight hint of something infernal about it...
Online Zero999
  • 0999
« Reply #10 on: April 07, 2024, 11:55:42 am »
Another thing is there will be a considerable capacitance between the two conductors,  so it's possible it will just charge up to a relatively low voltage when struck, then gradually decay, due to the parallel resistance created by the water.
Offline tooki
« Reply #11 on: April 07, 2024, 12:23:52 pm »
Hahahaha that autocorrect typo is too good to fix, so I’ll leave it!  >:D  >:D  >:D