I have been absent from the eeVBlog forum for some years and then my account disappeared, but have been watching Dave since about episode 30 and am always excited to see what is next to come. Hence, when I had a dreaded intermittent fault of my household electricity supply that was ultimately resolved I thought it would be great to share my experience on the forum. I am also hoping those in the know might be able to assist me in understanding exactly what has gone on.
Here’s the low down. Over the past few years my safety switch (RCD in the main board) would occasionally trip. Only once every six months or so. I would look around my property and find nothing unusual. Switch it back on and, yay, continue on for months with no issues.
Last night, however, things got a little more complicated. I awoke to a house of no power. Actually I awoke to the alarm on my UPS telling me there was no power. I again went to my meter box and discovered a tripped safety switch and no fuses tripped. At mid-night my main concern was restoring power to two aquarium pumps and fridges so to not endure spoilt food and dead fish. This time when I switched the safety switch it tripped immediately again. I decided a good start would be to isolate the household circuits. This particular RCD (safety switch) fed into five switched fuses. All the household mains. Lighting was on a separate circuit and had a separate RCD. I quickly realised that by keeping fuse three off (the front of my house circuit), I as able to keep the RCD on and continue trouble shooting.
Next step was to go inside where I switched off all appliances on that circuit at the wall and then was able to reinstate fuse three. I was then able to turn on my aquarium filters/heaters and return to bed knowing in the morning I had trouble shooting to do. I was betting it was a refrigerator on this line.
On waking I resumed my trial and error, hoping to identify the appliance at fault. I was eventually able to turn on everything on this circuit with no trip. I thought, “Great, the dreaded intermittent fault.” Then I went to turn my central heating on and bang, RCD tripped and no power. Strange thing was that the heater was on fuse four. I discovered this quickly as I could not turn the RCD back on without disabling fuse four. Next step was to go in the roof and disable the central heating at the main source again. It appeared I had success, for 30 minutes anyway. Next the RCD tripped again and again could not be restored without disabling the fuse four circuit. Here I was thinking it was fuse three. More trial and error of turning things off at the mains only to discover the fault now appeared to be at the back of my house.
In between all this I had contact about nine local electricians with no reply. Number ten was the lucky shot and finally I had a sparking on the way. I was total frustrated with the apparent lack of logic that I could apply to the problem. I knew somewhere I needed to review to total leakage current running through the RCD and this was going to be left to the sparky. One strange thing I noticed in my testing was when plugging in a power board into another power board that was switched off. This tripped the RCD. Initially I was confused thinking that this was off and should not cause a problem. This was my first clue once a level head returned.
My excellent sparky quickly measured the main power box and found a problem with leakage current. He seemed surprised when I was relieved and I explained that I was concerned we would be continuing my trial and error and waiting for this dreaded intermittent fault. He had me go throughout the house unplugging everything. I suddenly realised where my testing was at fault. I had not been disconnecting the neutral or earth.
It was not until every plug was out that I got a message that the fault had cleared. The last of these was a pond water pump. The next task was to slowly plug in each device and await a good and bad message. Good and I left it in. Bad and I left it out. This is where I am hoping the forum community to assist my understanding. Eventually we discovered that every surge protected power board was contributing to the leakage current as well as my pond pump (which I had already suspected). Everything else was fine. The explanation provided seem to make sense. A blasted power surge, pun intended. It seemed to have taken out every surge protected power board in my home, but nicely protected all the attached appliances. And I decided the pond pump would need review later.
Next I observed resistance measurements of all the suspect boards across neutral and ground. Was this what is called a neutral-ground bond?? Essentially, most of my power boards had anywhere from 20Meg to 1Meg across neutral to ground and were deemed damaged. I confirmed these by measuring them myself later. Only three were passed and they were open circuit across neutral to earth. My spark advised me two solutions. One was to replace all the suspect power boards damaged by presumed surge and, two, to test with plugs out from now on.
I think what was happening was a cumulative effect which had not entered into my logic. Different combinations of connections were giving random total residual current readings (leakage) and occasionally this would reach a threshold and trip.
I have since replaced all my suspect power boards and have had no further trips today. When I measured the NG resistance I was shocked to find this one board with 1MOhm. Seems high, but not when across the mains. Even 1MOhm from live to neutral.
Please forum patrons. Does anyone have any other thoughts on this? Is my basic understanding reasonable? My knowledge of electronics is reasonable, but I have always struggle with common mode issues. If I am right about this then does this mean that when I next have a power surge my surge suppressors might work, then fail in this way eventually accumulating leakage again? My now surge suppressor boards have an apparent light on them that is to go out when they are no longer functional. Isn’t this when a total fail occurs and before that MOVs may slowly degrade.
Has anyone else experienced this and is measuring the neutral to ground resistance a reliable way a determining a failed power board? Any suggested reading would be most appreciated. Sorry for the long post. Perhaps you found it intriguing.
Michael.