Dave suggested I drop my comment here , so no stones Please! I know it is off topic somewhat!
Problem: I started gathering information about 15 years ago, on applying power factor correction capacitors on large 850 KW and more , to save fuel. At the time it seemed logical.
That was 15 years ago. I never did it due to issues I have seen with hardwired applications on main grid power. On grid power you pay the penalty for low PF. So it works.
I could see that the caps could help a little in certain areas , but the maintenance to keep this running smoothly were not applicable. No maintenance programs for this bunch!
I could never find and engineering brief on the subject of fuel savings regarding portable generator sets. Did find very few mentions, but the Dave "BullShit", kicked in.
Well about a year ago , I heard that someone was adding 800 Kvar switch bank on a portable plant with a 2000 amp main at generator. So i put my ear to the ground for a year or so to see
what kind of results were achieved. From what little data I can obtain , the customer states that a fuel savings of 25% have been obtained. Wow, I thought. All the studies I did 15 years indicated only 3 to 5%. And you had to maintain the hell out of that and really keep and eye on its operations.
I did not ever install them on a genset because I was concerned of damage or runaway speed control of the genset.
Over the last 6 months, I have heard the genset has had 3 or 4 main Catipillar, 2000 amp circuit breaker failures. It was an electronic controlled circuit breaker and all were brand new! Why did these breakers fail? I immediately thought back to some of my research and wondered if the Kvar or magnetic Flux was flowing back and forth between the genset windings or stator and causing the trips. But why a breaker failure where the unit would not reset. No word as yet from Cat. The engineer that programmed the auto step capacitor bank had it cranked right up to 97% for the caps. I have heard of many problems once unity was crossed, leading pf over 1. Still what would cause this. Or does it really happen that way as far as flow back and forth between cap and windings.
I do remember reading one article regarding megawatt generators where a design engineer demanded the capacitor be removed from the system before switching in and out of grid power contacts. He never stated why. Also there are some articles where UPS systems do not like all the caps or switching.
My conclusion is,,(just a thought), if the portable plant is running at max or average load of 80% or so and a certain amount of capacitors are switched in,ONLINE, and someone in the field activated the ESTOP button, All currently loads are opened immediately, the genset is running wide open and the banks of Kvar are pulled in.
All of a sudden that magnetizing current flows into the genset windings or stator causing all kinds of crap. Strangely , no other damage has been reported. But after a few of these trips , it seems the new circuit breakers cannot handle the condition. ( They will not manually reset), The large flat platted blades of the circuit breaker appear to have some heat thermal color change on line and load bus.
Anyone have some hard core DAVE TYPE evidence of this or what is really happening?
Thanks to you all,
PS if this tread takes off a little , I will add a picture of the Circuit Breaker for funnzies.
Rix