Light fixtures periodically flickering in sync

(1/2) > >>

saratoga:
I have some light fixtures in my house that will periodically all start synchronously flickering at a slow rate (5-10 Hz) for a couple seconds and all stop at the same time.  They're definitely in phase and they all use the same model of driver, which has an annoying shape that would be hard to place with swapping junction boxes and cutting bigger holes in my wall. 

I tried bypassing the dimmer switch, but it has no effect.  10% brightness, 100% brightness, and no dimmer at all do it just the same, so not the dimmer switch. 

Since they flicker in sync, there must be a common source of interference to synchronize them.  Since they are dimmable, my theory is that some higher frequency signal on the power lines interferes with the phase cut detection circuit, causing the driver to lower the current briefly.  I don't have probes handy that can check mains power, and I'm not too excited about blowing up my scope anyway, but interference on the line seems a lot more likely than RF interference.

Would something like this help?

https://www.digikey.com/en/products/detail/qualtek/851-05%2F006/739530

And would it be up to code to put it in a junction box behind a light switch?  Or am I thinking about this wrong?

EPAIII:
Speaking from experience, I would suggest driving around your neighborhood, following the electric lines to the sub-station that serves your house. I wold not be surprised if you find some tree branches or vines that have grown into the higher Voltage lines. A tree branch swinging in the wind will have a natural frequency so your power can flicker at that rate.

Power companies just love to save money by cutting back on tree trimming.

Take some photos and send them to the power company. Threaten to sell them to a local TV station if they don't get on the ball.

jonpaul:
Typical of mains browout (temp drop in V) due to large load eg industrial motor starting.

Get a mains V monitor ($15) see V during the event, use a UPS for affected lights.

Any industry eg auto body welders, food manufacturing, chemical plants nearby?

j

jpanhalt:

--- Quote from: saratoga on March 29, 2024, 12:24:05 am ---
And would it be up to code to put it in a junction box behind a light switch?  Or am I thinking about this wrong?

--- End quote ---

One of my daughters had the same problem.  The problem was the dimmer switch.  You seem to have determined that was not the problem.  Are you absolutely sure?  The lights were LED.  I installed a 60W incandescent bulb and flickering stopped.  That was a key clue.

As for whether modifying the box is code, that can be complicated.  There are no limits on maximize size for the switch box so far as I know.  There are limits on the number of wires in a box based on size, as I am sure you know.  Can the  current box be replaced with a larger/deeper box?  There are face mounted boxes for repairs.  When it comes to modifying a box, that can be tricky.  Some inspectors will cite you even for drilling an extra hole.  There are box extenders that are code.

David_AVD:
Does the electricity company use ripple control for off-peak loads in your area? These are slow pulsed tones superimposed on the mains that can affect some devices. They would be present at roughly the same (multiple) times each day.

The effects are usually more pronounced with lights that are on dimmers or poor quality LED lights. You can sometimes also hear the tones in audio systems.