I didn't want to necromance the last topic we had on this (EV cement truck fire) - but the fire report from the car park fire at Luton Airport has now been released. This fire resulted in the total destruction of Car Park 2 and the vast majority of vehicles within were lost (a few were recovered from the roof). No one was injured.
https://www.bedsfire.gov.uk/sites/default/files/2024-10/Significant%20Incident%20Report%20LLA%20Car%20Park%202%20fire.pdfOrigin of the fire:"The fire originated in a privately owned car powered by a diesel fuelled internal combustion
engine with the cause of fire determined to be accidental."
"The initial 999 call was ‘received by Bedfordshire FRS Service Control at 20:47:20 hrs by
Crew Manager Service Control B from the driver of the Range Rover that was on fire. When
questioned by Service Control, the caller advised their car was a diesel Range Rover that it
was located on the third floor.’ The subsequent fire investigation confirmed that the vehicle
was powered by a diesel non-hybrid internal combustion engine"Conspiracy theories about this being a fire in a hybrid or converted car appear to be nonsense. It definitely wasn't an electric car. It's unlikely the exact cause will be determined (there's probably nothing left but the body shell); the origin appears to be around the engine area of the vehicle, and it occurred whilst the vehicle was in motion, so the possibility of an engine fault or a fuel rail leaking is there. The driver noted that they had been driving for two hours without issue before the fire; if the vehicle was driven for a period of time on the motorway (Luton Airport is very well connected to a motorway) it is likely that components will have been under load for some time and perhaps the sudden cooling down caused an oil seal to fail, or a fuel rail leak occurred at that moment.
On fire spread in car parks:"As they were making their way up the vehicle ramp from the second to the third floor BA
Team Alpha 2 observed that the fire was spreading to the second floor due to running fuel
and they retreated to extinguish this fire.""Initial crews from Bedfordshire FRS have indicated they witnessed “running fuel fires”. This
is where fuels such as petrol and diesel have escaped from fuel tanks. Most modern vehicles
are manufactured with plastic fuel tanks, these are more susceptible to failure in the initial
stages of a developing fire. It was confirmed that the Range Rover involved was fitted with a
plastic fuel tank. Heat of the developing fire will have been sufficient to ignite some of these
fuels as they followed the sloping gradient of the roadway surface, spreading ignitable fuel
beneath vehicles and into the drainage system thus spreading to other floors beneath the
point of origin.""On investigation looking through images taken by crews inside the car park it is evident
that drainage pipes within the car park are of plastic construction. The heat from the fire
and the running fuel fires entering the drainage system would have caused the pipes to
fail leading to fire spread."Whether electric vehicles contributed significantly to the fire:"In the immediate aftermath of the incident there was considerable speculation within the
press and across social media platforms about the fire originating from an electric vehicle
(EV). This was despite statements at the time from Bedfordshire FRS stating that the Service
believed the vehicle to a be a diesel vehicle. Subsequently it has been confirmed by the
fire investigation report that the fire originated in a diesel vehicle and the cause was
accidental.""Similarly, the fire investigation report for Luton airport identifies running fuel fires and an
approximately 10 mph wind along with the design of the car park with narrow gaps between
the parked cars as being the factors contributing to the spread of the fire. The 10mph wind
is based on a reading taken in Luton at a lower level, it should be noted that London Luton
Airport is located at the top of a hill and fire was on the third floor."It should be noted the author of the report doesn't specifically eliminate EVs as contributing to the spread, but crews reported running fuel fire as being the greatest hazard. Such fires would be non-existent with EVs, and fire could only spread between vehicles by direct thermal exposure. However, they do cite a report from the Norwegian fire authorities on a similar incident where wastewater from the fire was tested for quantities of lithium and cobalt:
"When it comes to the fire’s environmental impact, analyses of water samples in nearby water
bodies provide indications on the contribution of electric vehicle batteries (analyses carried
out by COWI,). The analyses included lithium and cobalt, main components of an electric car
battery. Lithium was not found in any of the water samples, and the analyses showed low
concentrations of cobalt. This indicates that batteries from burnt out electric vehicles have
not contributed to the pollution of nearby water bodies."
"Observations made during the fire, as well as water analyses in retrospect, thus imply that
electric car batteries were not involved in the fire. However, technical investigations of the
actual batteries of the burnt-out or partially burnt-out electric and hybrid vehicles are
necessary to substantiate this point and provide a definite answer."TL;DR - there's no direct evidence of contamination due to burning batteries, but it's impossible to say certainly at this stage that EV batteries
weren't involved. However, the fire crews don't seem particularly bothered by this, and highlight lower risk (emphasis mine).
"Regardless of the type of engine the fire load of a car is significant. As such, if a car
catches fire there is a strong possibility of the fire spreading to adjacent vehicles. The
open sided design of most multi storey car parks means that wind can become a
contributing factor in the fire spread. The issue of running fuel fires does not occur with
electric vehicles."Perhaps this will quell some of the speculation on EV fire risk... but I'm sure we'll still see plenty of YouTube posts from the likes of AutoExpert and friends about how this is the biggest risk ever in new vehicles and we'll all be seeing Tesla's bursting into flames left, right and centre if we don't stop them now and go back to those totally non-flammable combustion engine cars.