Hi everyone,
I'm trying to power a reflow oven but am running into power issues with the standard Canadian wall outlet. I didn't realize this but the limit for the wall outlet is usually less than 15 A at 120 V AC (the oven requires approximately 2400 W and is configured for 110 V AC input). So, my next go to solution was thinking of connecting the reflow oven to the NEMA 14-30 wall outlet used for the dryer (I'm still reading up on how the NEMA 14-30 is wired and if other possible solutions exist using regular wall outlets). I was also wondering if there is a device that will connect multiple wall outlets with different phases/fused networks and can provide one single 110 V AC with boosted power.
Has anyone ran into a similar issues and if so, how were you able to solve it? Any advice would be greatly appreciated!
Although your original idea should work with the 30 amp outlet, you could be violating electrical codes in your area by doing this. You need to view this special circuit from end to end. Start with a 30 amp breaker, the wiring should be rated at 30 amps as well (10 AWG). The next step is calculating voltage drop under load based on the length of the wiring run.
Secondarily, in your case, the power cord to the device needs to be rated for at least 20 amps, so the power cord wire gage needs to be at least 12 AWG. The power plug on the device needs to be rated at minimum 20 amps as well.
This leads me to ask the obvious question: Is the device rated for 120/240 volts depending on heating element wiring configuration? I would definitely check this out. If the electronics control is 120 VAC then a 240 VAC circuit is simply 2 - 120 VAC circuits (at 180° phase difference). This is not a problem if part of your device is depending on a 120 VAC input (i.e. a 120 VAC hot and a neutral) because the NEMA 14-30 is a 4 wire receptacle. Even if the device can be driven with 240 VAC, which would then only be a 10 amp draw, according to code, your receptacle circuit will still need to meet the 30 amp requirement which means 10 AWG wire. This is for safety in case someone plugs a 30 amp device into this receptacle.
Many devices with multiple elements can be rewired in either a series or parallel configuration to meet voltage/current requirements. It is simply a matter of moving jumpers to reconfigure the element input voltage. For example, a device with 2 elements in parallel that produces 2400W at 120 VAC can be reconfigured to produce 2400W at 240 VAC by rewiring the elements into series.
Hope this helps...