Zero999:
--- Quote from: martincho on March 10, 2022, 01:23:00 am ---I heard back from the company. The contacts are the same on the 230 and 440 V versions. They said the neon lamp is likely to blow out at 480.
I think I'll get one and run a torture test at 480 and see how much trouble I can get into. I like the design. It's good to know the contacts are not an issue. The rest is manageable.
Of course, they disclaim any responsibility when used outside of specifications, which is fine with me.
--- End quote ---
It should be fine at 480V. Increase the resistor value, to protect the neon lamp.