Author Topic: RCD / GFCI finger test?  (Read 14502 times)

0 Members and 1 Guest are viewing this topic.

Offline StonentTopic starter

  • Super Contributor
  • ***
  • Posts: 3824
  • Country: us
RCD / GFCI finger test?
« on: March 02, 2015, 06:06:26 pm »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger?  Did you actually feel it?

I've seen videos demonstrating a hot dog being used as a test but surprised YouTube has not provided anyone doing it for real.
The larger the government, the smaller the citizen.
 

Offline Artlav

  • Frequent Contributor
  • **
  • Posts: 750
  • Country: mon
    • Orbital Designs
Re: RCD / GFCI finger test?
« Reply #1 on: March 02, 2015, 06:26:14 pm »
but surprised YouTube has not provided anyone doing it for real.
I guess it's because you don't test emergency saw blade retraction system by sticking your arm across it.  :-//
 

Offline electr_peter

  • Supporter
  • ****
  • Posts: 1301
  • Country: lt
Re: RCD / GFCI finger test?
« Reply #2 on: March 02, 2015, 08:14:56 pm »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger?  Did you actually feel it?
I have not done that on purpose and would not want to do that. I imagine what it would feel like, though (from experience...). It is dangerous lottery you are playing (depending on many factors). Also, remember that current is not limited in any way during those 20ms.
Quote
I've seen videos demonstrating a hot dog being used as a test but surprised YouTube has not provided anyone doing it for real.
They are either cowards or not stupid enough to try it.
 

Offline dexters_lab

  • Supporter
  • ****
  • Posts: 1890
  • Country: gb
Re: RCD / GFCI finger test?
« Reply #3 on: March 02, 2015, 08:58:42 pm »
i'm surprised there is no video of it either... maybe drop a note over to Mehdi Sadaghdar, maybe he would try it?

knowing what uk mains feels like, 20ms is just going to be a quick jolt, still... i dont fancy trying it!

Offline amyk

  • Super Contributor
  • ***
  • Posts: 8262
Re: RCD / GFCI finger test?
« Reply #4 on: March 02, 2015, 11:51:15 pm »
but surprised YouTube has not provided anyone doing it for real.
I guess it's because you don't test emergency saw blade retraction system by sticking your arm across it.  :-//
Funny you say that, there's a video on YouTube of the inventor testing his sawblade retractor with his own finger.
 

Offline BradC

  • Super Contributor
  • ***
  • Posts: 2106
  • Country: au
Re: RCD / GFCI finger test?
« Reply #5 on: March 03, 2015, 12:24:53 am »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger? 

Yes. Not intentionally of course (thats what test buttons are for!)

Did you actually feel it?

Absolutely.

30mA across a finger is a *lot* of current. It hurts just like any other electric shock, it's just a lot shorter as it cuts off the juice faster than your normal retraction reaction. More of a stab than a good belt.
I've been thinking of picking up a couple of 10mA medical grade units for my bench, but the best policy is to try not to get whacked in the first place. We don't have RCD's in the house yet. I have them in the shed (new sub-board), and I have plug in units for my bench.

 

Offline StonentTopic starter

  • Super Contributor
  • ***
  • Posts: 3824
  • Country: us
Re: RCD / GFCI finger test?
« Reply #6 on: March 03, 2015, 01:46:02 am »
but surprised YouTube has not provided anyone doing it for real.
I guess it's because you don't test emergency saw blade retraction system by sticking your arm across it.  :-//
Funny you say that, there's a video on YouTube of the inventor testing his sawblade retractor with his own finger.

The only one I've ever seen with that was using a hot dog.
The larger the government, the smaller the citizen.
 

Offline StonentTopic starter

  • Super Contributor
  • ***
  • Posts: 3824
  • Country: us
Re: RCD / GFCI finger test?
« Reply #7 on: March 03, 2015, 01:50:39 am »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger?  Did you actually feel it?
I have not done that on purpose and would not want to do that. I imagine what it would feel like, though (from experience...). It is dangerous lottery you are playing (depending on many factors). Also, remember that current is not limited in any way during those 20ms.
Quote
I've seen videos demonstrating a hot dog being used as a test but surprised YouTube has not provided anyone doing it for real.
They are either cowards or not stupid enough to try it.

Well I've been socked at least 3 to 5 times from 120V AC but it's always been limited to one hand.

More times than that though I've been shocked by some other amount of electricity that was a reduced form the 120V AC.

At a house I used to live in, I would get a shock any time I touched the cable modem line.   I think I tested it and it was between 40 to 60 volts AC, not sure how it happened though.

I've also been shocked when some current was leaking across a computer's chassis and I unplugged a cable that was grounded on the other side.
The larger the government, the smaller the citizen.
 

Offline RJFreeman

  • Regular Contributor
  • *
  • Posts: 207
  • Country: au
    • Australian Technical Production Services
Re: RCD / GFCI finger test?
« Reply #8 on: March 03, 2015, 01:55:08 am »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger?  Did you actually feel it?

Yep, I have tripped one (not deliberately)  and yep, damn right you feel it  :o ....
 

Offline StonentTopic starter

  • Super Contributor
  • ***
  • Posts: 3824
  • Country: us
Re: RCD / GFCI finger test?
« Reply #9 on: March 03, 2015, 02:19:19 am »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger?  Did you actually feel it?

Yep, I have tripped one (not deliberately)  and yep, damn right you feel it  :o ....

In the US, they are typically found on outlets that are near sinks, but rarely elsewhere.

I never really understood what they did until more recently in life.  I had always thought they had something to do with tripping if you were to drop a hair dryer into the sink, but unless the hair drier has its own built in rcd, it won't do anything, the hair drier will just put load on the live and neutral and as long as it doesn't exceed the normal 15 to 20 amp breaker rating, nothing will happen at all.

I just assumed they were like a normal circuit breaker, but now understand they measure imbalance between live and neutral, indicating you may have come in contact with ground.

This one here says they trip at 5mA.

http://www.thisoldhouse.com/toh/article/0,,249536,00.html
« Last Edit: March 03, 2015, 02:20:58 am by Stonent »
The larger the government, the smaller the citizen.
 

Offline codeboy2k

  • Super Contributor
  • ***
  • Posts: 1836
  • Country: ca
Re: RCD / GFCI finger test?
« Reply #10 on: March 03, 2015, 03:55:03 am »
Yeah, they should trip at much much less than 30mA.   5mA seems about right.

When I lived in the US, my house had them in the bathroom, in the kitchen, in the garage, and outdoors. Each single RCD/GFI device controlled a downstream daisy chain of about 3-4 ordinary sockets.

I'm in Canada now, and surprisingly there is not much in this current home.  I actually put them in myself here at the kitchen and bathroom, and one on my bench.  This house is older though, about 1970's so it's probably understandable.

 

Offline Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: RCD / GFCI finger test?
« Reply #11 on: March 03, 2015, 04:41:49 am »
5mA is fine for single-outlet protection of devices or circuits with no electronics or contact with water (tumble dryer, anyone?). It's hopeless for protecting general purpose circuits.
 

Offline BradC

  • Super Contributor
  • ***
  • Posts: 2106
  • Country: au
Re: RCD / GFCI finger test?
« Reply #12 on: March 03, 2015, 04:52:31 am »

This one here says they trip at 5mA.

http://www.thisoldhouse.com/toh/article/0,,249536,00.html

And it's half right. Like a thermal circuit breaker, it's a cumulative system. The more currently leakage, the faster it will trip. So at 30mA you will get your 20ms. At 5ma it might take 5 seconds. Your average household RCD is a 20-30mA device. To go lower than that you start getting into medical grade devices for exactly the reason Monkeh states. All domestic devices leak to some degree, but some more than others. Outside of realy leakage (like moisture or degrading motor insulation), most issues with tripped RCD's seem to be badly designed mains input filters that leak on switch-on. Usually a big enough spike to trip the rcd at start up, but not steady state. I've seen really bad CFL's do this enough that having more than 2 or 3 on the same switch will trip the RCD every time they are switched on.

Nothing worse than coming home from holiday to a tripped RCD and a stinky fridge/freezer.
 

Offline amyk

  • Super Contributor
  • ***
  • Posts: 8262
Re: RCD / GFCI finger test?
« Reply #13 on: March 03, 2015, 04:52:56 am »
but surprised YouTube has not provided anyone doing it for real.
I guess it's because you don't test emergency saw blade retraction system by sticking your arm across it.  :-//
Funny you say that, there's a video on YouTube of the inventor testing his sawblade retractor with his own finger.

The only one I've ever seen with that was using a hot dog.
Seek to 4:00 to see his finger go in.
 

Offline RJFreeman

  • Regular Contributor
  • *
  • Posts: 207
  • Country: au
    • Australian Technical Production Services
Re: RCD / GFCI finger test?
« Reply #14 on: March 03, 2015, 04:54:24 am »
Quote
This one here says they trip at 5mA.

http://www.thisoldhouse.com/toh/article/0,,249536,00.html

RCDes (GFCIes) come in different sensitivities, between 5 and 30mA are usual for for protection against electrocution but are considered to be in the  'High sensitivity' group.

Fixed household ones in Australia are typically 30mA
« Last Edit: March 03, 2015, 04:57:51 am by RJFreeman »
 

Offline pickle9000

  • Super Contributor
  • ***
  • Posts: 2439
  • Country: ca
Re: RCD / GFCI finger test?
« Reply #15 on: March 03, 2015, 05:10:41 am »
RCDs tend to trip in about 20ms at about 30mA of current. Has anyone ever tripped one via direct contact with a finger?  Did you actually feel it?

I've seen videos demonstrating a hot dog being used as a test but surprised YouTube has not provided anyone doing it for real.

I have tripped one (120v) and while not painful certainly got my attention and felt it though my entire arm. This was a bench mounted one and I use it for safety.

Compared to a regular shock it was mild to nothing. I have done that twice at 120v and once at 240 (very painful). Even though I was taking precautions the events happened a long time ago, no injury. Not recommended though.
 

Offline electr_peter

  • Supporter
  • ****
  • Posts: 1301
  • Country: lt
Re: RCD / GFCI finger test?
« Reply #16 on: March 03, 2015, 07:34:54 am »
I will stress this again - fault current is not limited in any way to 5mA or 30mA until RCD trips in few tens of ms (hopefully).

Without an RCD, it would feel like a jolt going through an arm and leave tingling sensation (and your muscles/reaction play an RCD role - meaning 100-500ms of joy). If RCD trips in 20ms, you will feel very short pulse and have some seconds to think about life.

Still, it is not a recommended way to test RCD/GFCI circuits. Not a good way to find a stuck contact.
 

Offline Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: RCD / GFCI finger test?
« Reply #17 on: March 03, 2015, 07:36:48 am »
Still, it is not a recommended way to test RCD/GFCI circuits. Not a good way to find a stuck contact.

Or the various other methods of failure.

RCDs are great devices to have, very worthwhile. But they are meant to be the last line of defence.
 

Offline SteveyG

  • Supporter
  • ****
  • Posts: 987
  • Country: gb
  • Soldering Equipment Guru
Re: RCD / GFCI finger test?
« Reply #18 on: March 03, 2015, 07:41:08 am »
It is dangerous lottery you are playing (depending on many factors). Also, remember that current is not limited in any way during those 20ms.

The other thing to remember, is there's nothing to say the current through you will reach 30mA. You may end up gripping onto a conductor, but because of what you're standing on or what footwear you have on the current through you gets no higher than 20mA for example, leaving you unable to let go.  :-- :--
YouTube Channel: https://www.youtube.com/user/sdgelectronics/
Use code: “SDG5” to get 5% off JBC Equipment at Kaisertech
 

Offline Monkeh

  • Super Contributor
  • ***
  • Posts: 7992
  • Country: gb
Re: RCD / GFCI finger test?
« Reply #19 on: March 03, 2015, 07:42:34 am »
It is dangerous lottery you are playing (depending on many factors). Also, remember that current is not limited in any way during those 20ms.

The other thing to remember, is there's nothing to say the current through you will reach 30mA. You may end up gripping onto a conductor, but because of what you're standing on or what footwear you have on the current through you gets no higher than 20mA for example.  :-- :--

Which is generally accepted not to be lethal for an adult, and won't prevent you from detaching from the source of the shock.
 

Offline SteveyG

  • Supporter
  • ****
  • Posts: 987
  • Country: gb
  • Soldering Equipment Guru
Re: RCD / GFCI finger test?
« Reply #20 on: March 03, 2015, 11:05:55 am »
It is dangerous lottery you are playing (depending on many factors). Also, remember that current is not limited in any way during those 20ms.

The other thing to remember, is there's nothing to say the current through you will reach 30mA. You may end up gripping onto a conductor, but because of what you're standing on or what footwear you have on the current through you gets no higher than 20mA for example.  :-- :--

Which is generally accepted not to be lethal for an adult, and won't prevent you from detaching from the source of the shock.

Depends very much on the individual. It's not considered lethal in terms of being unlikely to cause ventricular fibrillation, but over a relatively short period of time will kill you and is incredibly painful.
YouTube Channel: https://www.youtube.com/user/sdgelectronics/
Use code: “SDG5” to get 5% off JBC Equipment at Kaisertech
 

Offline Zero999

  • Super Contributor
  • ***
  • Posts: 19491
  • Country: gb
  • 0999
Re: RCD / GFCI finger test?
« Reply #21 on: March 03, 2015, 12:35:08 pm »
There's a small risk the RCD may fail to trip.

This is probably why isolation transformers are used for shavers here in the UK, rather than RCDs because they're passive components and don't rely on anything mechanical.

Neither isolation transformers nor RCDs are perfect but I'd feel more comfortable putting my finger between an isolation transformer and earth than an RCD and earth.
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 7752
  • Country: de
  • A qualified hobbyist ;)
Re: RCD / GFCI finger test?
« Reply #22 on: March 03, 2015, 01:02:24 pm »
5mA is fine for single-outlet protection of devices or circuits with no electronics or contact with water (tumble dryer, anyone?). It's hopeless for protecting general purpose circuits.

Yep, and you also got the Y class filter caps (SMPS for example) which pass some current to earth. A few SMPSs and you'll have more than 5mA loss by the Y caps. Therefore there's a capacitance/current limit for the Y caps over here, to keep the current loss reasonable. IIRC, the maximum current allowed is 3.5mA for usual devices (some special stuff got different limits).
 

Offline HackedFridgeMagnet

  • Super Contributor
  • ***
  • Posts: 2028
  • Country: au
Re: RCD / GFCI finger test?
« Reply #23 on: March 03, 2015, 01:24:21 pm »
I will stress this again - fault current is not limited in any way to 5mA or 30mA until RCD trips in few tens of ms (hopefully).
Sorry I am just being pedantic but of course the fault current is limited.
It is limited by the source impedance.
I am not sure what the fault current would be after say 25ms though.

It is also generally less than the advertised tripping current. So in some cases the fault current may not even reach 30mA.
 

Offline electr_peter

  • Supporter
  • ****
  • Posts: 1301
  • Country: lt
Re: RCD / GFCI finger test?
« Reply #24 on: March 03, 2015, 02:04:58 pm »
I will stress this again - fault current is not limited in any way to 5mA or 30mA until RCD trips in few tens of ms (hopefully).
Sorry I am just being pedantic but of course the fault current is limited.
It is limited by the source impedance.
I think my statement was misunderstood. Of course you could say current is limited by source and circuit impedance as in any other circuit. But that is not active or even passive current limiting in a real sense that is helpful for poor person on GFCI/RCD socket. In fact source impedance is made as low as possible for an equipment grounding purposes so I would say there is no current limiting what so ever.

RCD/GFCI monitors fault current and trips if its too high, but again, it does not limit current in any way until that happens.
 


Share me

Digg  Facebook  SlashDot  Delicious  Technorati  Twitter  Google  Yahoo
Smf