Hi folks, is any refrigeration expert here, or maybe just someone with better searching skills.

I'm trying to find out how are electronic expansion valves controlled in systems without pressure sensors when you have only temperature sensors.
With a pressure sensor, it is simple, you can calculate superheat and just open the valve more to decrease it.
But cannot find how they do it from temperature only, do they estimate pressure based on evaporator inlet temperature?
 

Offline NiHaoMike

  • Super Contributor
  • ***
  • Posts: 9323
  • Country: us
  • "Don't turn it on - Take it apart!"
    • Facebook Page
Re: Refrigeration question - Expansion valve regulation strategy
« Reply #1 on: June 23, 2023, 12:36:27 pm »
But cannot find how they do it from temperature only, do they estimate pressure based on evaporator inlet temperature?
That's actually a very accurate way to measure the low side pressure in steady state operation.
Cryptocurrency has taught me to love math and at the same time be baffled by it.

Cryptocurrency lesson 0: Altcoins and Bitcoin are not the same thing.
 

Offline MiyukiTopic starter

  • Frequent Contributor
  • **
  • Posts: 908
  • Country: cz
    • Me on youtube
Re: Refrigeration question - Expansion valve regulation strategy
« Reply #2 on: June 24, 2023, 10:12:37 am »
But cannot find how they do it from temperature only, do they estimate pressure based on evaporator inlet temperature?
That's actually a very accurate way to measure the low side pressure in steady state operation.
It makes sense with proper coupling and insulation
I just wasn't sure if there isn't any hidden catch
Thanks
 

Offline NiHaoMike

  • Super Contributor
  • ***
  • Posts: 9323
  • Country: us
  • "Don't turn it on - Take it apart!"
    • Facebook Page
Re: Refrigeration question - Expansion valve regulation strategy
« Reply #3 on: June 24, 2023, 12:21:34 pm »
I have done it with a diode connected transistor and a TMP513. It was at least as accurate as my Yellow Jacket HVAC gauges. (That was despite the fact I used R433b and had to interpolate a PT lookup table.) Even getting the condensing temperature was pretty easy by putting the sensor in the middle part of the condenser.
Cryptocurrency has taught me to love math and at the same time be baffled by it.

Cryptocurrency lesson 0: Altcoins and Bitcoin are not the same thing.
 

Offline noidea

  • Supporter
  • ****
  • Posts: 209
  • Country: au
Re: Refrigeration question - Expansion valve regulation strategy
« Reply #4 on: September 29, 2023, 04:01:12 pm »
Hi folks, is any refrigeration expert here, or maybe just someone with better searching skills.

I'm trying to find out how are electronic expansion valves controlled in systems without pressure sensors when you have only temperature sensors.
With a pressure sensor, it is simple, you can calculate superheat and just open the valve more to decrease it.
But cannot find how they do it from temperature only, do they estimate pressure based on evaporator inlet temperature?

Sorry for the late reply I don't frequent the forum as much as I used to. There is nothing wrong with calculating Superheat by using sensors instead of transducers, most of the Japanese brands use this control for the expansion valve on their VRF indoor units. Two sensors minimum, midpoint of the coil for an approximation of evaporating temperature and exit of the coil for superheated temp. Better arrangements use an inlet sensor as well and calculate either Exit - inlet or Exit - midpoint to regulate the expansion valve. They will also ensure the inlet and midpoint sensors are on different circuits of the coil to take into account a blocked circuit. It all works great until you have a sensor that plays up and gives erroneous inputs when the unit is running...
You can calcualte superheat from sensors
 or I would have an
 

Offline MarkS

  • Supporter
  • ****
  • Posts: 855
  • Country: us
Re: Refrigeration question - Expansion valve regulation strategy
« Reply #5 on: September 29, 2023, 04:21:48 pm »
Hi folks, is any refrigeration expert here, or maybe just someone with better searching skills.

I'm trying to find out how are electronic expansion valves controlled in systems without pressure sensors when you have only temperature sensors.
With a pressure sensor, it is simple, you can calculate superheat and just open the valve more to decrease it.
But cannot find how they do it from temperature only, do they estimate pressure based on evaporator inlet temperature?

Non-electronic expansion valves use a sealed tube with a bulb at one end that is attached to the line set. It operates on temperature. The fluid in the bulb expands and contracts with the temperature of the line and moves a diaphragm in the valve to meter the refrigerant. Using a pressure sensor would just add complexity and expense to the system, not to mention a point of failure. Or to simplify: If it ain't broke, don't fix it.
 
The following users thanked this post: amyk

Offline MiyukiTopic starter

  • Frequent Contributor
  • **
  • Posts: 908
  • Country: cz
    • Me on youtube
Re: Refrigeration question - Expansion valve regulation strategy
« Reply #6 on: October 29, 2023, 05:08:25 pm »
Hi folks, is any refrigeration expert here, or maybe just someone with better searching skills.

I'm trying to find out how are electronic expansion valves controlled in systems without pressure sensors when you have only temperature sensors.
With a pressure sensor, it is simple, you can calculate superheat and just open the valve more to decrease it.
But cannot find how they do it from temperature only, do they estimate pressure based on evaporator inlet temperature?

Non-electronic expansion valves use a sealed tube with a bulb at one end that is attached to the line set. It operates on temperature. The fluid in the bulb expands and contracts with the temperature of the line and moves a diaphragm in the valve to meter the refrigerant. Using a pressure sensor would just add complexity and expense to the system, not to mention a point of failure. Or to simplify: If it ain't broke, don't fix it.

But those expansion valves work in pressure mode and the bulb adds superheat accuracy. Ones for bigger evaporators even use an external pressure tube (from the end of the evaporator, where the bulb is placed) to be more precise.
It is the same mode as when electronic ones use a pressure transducer.
 