Author Topic: Shocking induced voltage surprise(the importance of grounding)  (Read 3153 times)

0 Members and 1 Guest are viewing this topic.

Offline KalinTopic starter

  • Regular Contributor
  • *
  • Posts: 101
  • Country: ca
Working today I managed to get a quite a good shock off of a cable connector and I find the reason behind it very interesting.
 I am an electrician working in a plant with 600V 3-phase powering most everything in the mill. In some locations we use PVC junction boxes. I was very surprised when I opened up this PVC junction box to find everything neat and tidy with all of the grounding in place. I opened up the next box downstream of this cable and it was the same thing everything where it should be. But when the motor was running I was still reading 160V to ground from the connector. Long story short, with teck cable there was enough induced voltage in the steel armour on the cable to shock and because it terminated in a PVC box there was no path to ground until I came along. I had no idea that induction was that powerful and it definitely shows why electricity is nothing to mess with.

Hopefully someone finds this interesting/funny/informative.

 
 

Offline Dubbie

  • Supporter
  • ****
  • Posts: 1115
  • Country: nz
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #1 on: March 30, 2017, 11:12:51 pm »
I had no idea that induction was that powerful

You should try grabbing the output terminals of a 600V transformer. There is no connection at all to the input terminals. That will be a nice extension of your education about the power of induction.
It may however be the last lesson you ever have about the subject.
 

Offline KalinTopic starter

  • Regular Contributor
  • *
  • Posts: 101
  • Country: ca
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #2 on: March 30, 2017, 11:18:30 pm »



You should try grabbing the output terminals of a 600V transformer.
[/quote]

I should have said I had no idea that incidental induction was that powerful. A transformer is designed to transfer electricity through induction. Cable is not.



Sent from my SM-G930W8 using Tapatalk

 

Offline Dubbie

  • Supporter
  • ****
  • Posts: 1115
  • Country: nz
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #3 on: March 30, 2017, 11:20:26 pm »
I know thats what you meant. Was just poking a little fun

:D
 

Offline calexanian

  • Super Contributor
  • ***
  • Posts: 1886
  • Country: us
    • Alex-Tronix
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #4 on: March 30, 2017, 11:22:28 pm »
There are two modes of coupling. Induction and capacitive. Both are just as deadly. I have had to deal with both over the years and utility companies have had to institute specific procedures to avoid it.
Charles Alexanian
Alex-Tronix Control Systems
 

Offline KalinTopic starter

  • Regular Contributor
  • *
  • Posts: 101
  • Country: ca
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #5 on: March 30, 2017, 11:22:39 pm »
I know thats what you meant. Was just poking a little fun

:D
:) All good. I felt like quite the dumbass today so maybe I'm a little over sensitive.

In my brilliance after the first shock I reached out and touched it again just to be sure I hadn't imagined it.
 

Offline Cubdriver

  • Supporter
  • ****
  • Posts: 4201
  • Country: us
  • Nixie addict
    • Photos of electronic gear
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #6 on: March 31, 2017, 12:41:33 am »

:) All good. I felt like quite the dumbass today so maybe I'm a little over sensitive.

In my brilliance after the first shock I reached out and touched it again just to be sure I hadn't imagined it.

 :-DD :-DD  That sounds like something I'd do, too.   

:wtf:  Wait, did I really just get.. *bzzzzzt*     :rant: :scared: :rant:  :palm:

My vote would be for capacitive coupling, FWIW.

-Pat
If it jams, force it.  If it breaks, you needed a new one anyway...
 

Offline KalinTopic starter

  • Regular Contributor
  • *
  • Posts: 101
  • Country: ca
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #7 on: March 31, 2017, 12:45:27 am »

:) All good. I felt like quite the dumbass today so maybe I'm a little over sensitive.

In my brilliance after the first shock I reached out and touched it again just to be sure I hadn't imagined it.

 :-DD :-DD  That sounds like something I'd do, too.   

:wtf:  Wait, did I really just get.. *bzzzzzt*     :rant: :scared: :rant:  :palm:

My vote would be for capacitive coupling, FWIW.

-Pat
Do you mean it wasn't inducing voltage it was a result of the capacitive coupling? I will have to do some research to learn about this. I'm still an apprentice so I don't have all the school yet.

Wouldn't that much capacitance affect the operation of the circuit?
« Last Edit: March 31, 2017, 12:52:20 am by Kalin »
 

Offline Brumby

  • Supporter
  • ****
  • Posts: 12411
  • Country: au
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #8 on: March 31, 2017, 01:21:15 am »
In an environment where you are running 600V 3 phase - you would look like a mosquito in a bug-zapper.
 

Offline KalinTopic starter

  • Regular Contributor
  • *
  • Posts: 101
  • Country: ca
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #9 on: March 31, 2017, 01:34:23 am »
In an environment where you are running 600V 3 phase - you would look like a mosquito in a bug-zapper.
Just in general? Or if you actually touch phase to phase?

I think workmanship make the difference in safety. You can have a 120V Deathtrap or an uber-safe 600V distribution center, the difference being the workmanship and attitude towards safety
 

Offline Brumby

  • Supporter
  • ****
  • Posts: 12411
  • Country: au
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #10 on: March 31, 2017, 02:38:09 am »
In my book, the attitude towards safety comes first.  No matter how good the workmanship is, with a poor attitude, you can kill yourself - or worse, someone else.

Get the attitude right before all else.  When there are safety protocols in place - FOLLOW THEM.  Don't argue or feel they are slowing you down or wasting time.  They are there for a good reason.  You don't have to understand the why or how they came to be, although such knowledge might be helpful - just as long as you don't try and rationalise a way around them.

Good workmanship is part of this, so you should always endeavour to be spot on with this - but a word to the wise....  If you are approaching an environment for the first time, I would suggest it to be a sensible move to not assume anything, especially if I was going to be working on it.  Poor workmanship might be obvious, but it also may not.  Good workmanship is still subject to issues if, for example, something has been damaged - especially when that damage is out of sight.


As for the the 600V 3 phase environment...  Contact from phase to phase may not quite vaporise you - but you aren't likely to get a second chance.  At that voltage and with 3 phase, the equipment is going to be drawing a significant amount of power.  Get yourself in the wrong place and the power supply and equipment aren't going to suffer.

Pretty much the same for any capacitive or inductive coupling... and when you have long runs, the capacitance just increases, allowing for more current to pass.  Again, these currents (if they do flow) are going to be small compared to the demands of the equipment, so their impact is not likely to be much on the installation - but they could still be large enough to give you a toe tag.

Be safe.
« Last Edit: March 31, 2017, 02:46:28 am by Brumby »
 

Offline Gregg

  • Super Contributor
  • ***
  • Posts: 1156
  • Country: us
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #11 on: March 31, 2017, 03:33:23 am »
You may have more of a problem than capacitive or inductive coupling.  With all 3 phases carrying relatively balanced currents inside a metallic conduit, the AC coupling should be minimal capacitive or inductive.  That is the exact reason why it is mandatory to run all phases through the same conduit to cancel that type of coupling.  You might get a high reading on a high impedance digital meter but with a low impedance measuring device like a solenoid actuated meter it should go away.  I always carry a Knopp K-60 when working on mains power.
 

Offline KalinTopic starter

  • Regular Contributor
  • *
  • Posts: 101
  • Country: ca
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #12 on: March 31, 2017, 11:47:06 am »
You may have more of a problem than capacitive or inductive coupling.  With all 3 phases carrying relatively balanced currents inside a metallic conduit, the AC coupling should be minimal capacitive or inductive.  That is the exact reason why it is mandatory to run all phases through the same conduit to cancel that type of coupling.  You might get a high reading on a high impedance digital meter but with a low impedance measuring device like a solenoid actuated meter it should go away.  I always carry a Knopp K-60 when working on mains power.
I put grounding bushings on the teck connectors and it went away. I don't have a solenoid meter but my fluke does have a low impedance setting would that work well enough?
 

Offline Damianos

  • Frequent Contributor
  • **
  • Posts: 268
  • Country: gr
Re: Shocking induced voltage surprise(the importance of grounding)
« Reply #13 on: March 31, 2017, 07:20:15 pm »
I think that is capacitive and not inductive coupling.
I am thinking that the circuit has somewhere to close...
When you touched the connector your body closed the circuit to ground putting yourself in series with the capacitor:
ground - power circuit - wires to motor -| |- cable shield - body - ground
Due to relatively low capacitance the voltage dropped with even a little load. This can be checked by connecting a resistor of few kOhms in the place of "body" and measuring the voltage again.

If it was inductive coupling then the secondary coil (the shield of the cable) has to be connected to ground on the other end. In this case the load (body) is connected in parallel with the that coil, that has very low impedance (it is one turn at low frequency). You can imagine what would happen by touching it or by grounding it.

 