I used to buy thermocouple extension wire in kilometer reels....... But all the solar sensors I have seen use a NTC or PTC thermistor that typically is 10k at 25C. Thermocouples are really not a good thing when you want to sense within 100C of ambient, the cost to get an accurate reading is way too high for the associated electronics and they need calibration to match the sensor to the input. RTD and thermistor are easier, as they have both a larger signal and are easier to interface, you have signals in the range of 100mV to 5V, as opposed to measuring a signal of 100microvolts or less. You can also have then with a 1% or less initial error and a no calibration install is possible.