I have a Hunter fan with a four lights lamp kit.   Installed a few years ago.   Currently with three incandescent buklbs and one compact fluorescent.   No dimming.   Minutes ago, as it was getting darker, I turned it on.    To my surprise, it took a split second to go on, which was abnormal.  Then after another split second it went off, and then on, off... with a steady flashing pattern.   A bit faster than once per second.   It is not flickering.

Wondering about the fluorescent bulb, I removed it, making no difference.   My wife removed the rest of the bulbs, swapping the last one, with no difference.

I believe the same circuit has two smoke alarms in it, but I do not see how they can have any part in the magic.   

Any ideas as to what the cause would be?     Am I in an encounter of the third kind?    Can you point me to a paranormal detector circuit?   I'd hate to have to call Ghost Busters!
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Ian.M on October 15, 2016, 12:00:12 am
Bad contact + thermal expansion, probably of the copper wire, due to the contact resistance.  When it gets hot enough its moved enough to make full contact till its cooled some.

Its currently a fire hazard so do *NOT* use again until you've dismantled it and checked for overheated wires and loose connections.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 15, 2016, 01:57:56 am
I have it off.    I thought of the fire hazard.   I was thinking of some thermal effect, but I was thinking that it would be more like current goes through and goes on first, then warms up and disconnects.  It cools off and reconnects.    The opposite threw me off.

What you are saying is that there is a poor contact, not enough to bring the bulbs on, but enough to provide heat for the cycle.

I will look at the connections on the hanging box.   I was wondering about the breaker as a possibility.    I will recycle it first. 
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Ian.M on October 15, 2016, 03:24:27 am
Its unlikely to be the breaker, but probably not impossible.   It wouldn't hurt to check it with a known good bulbholder and bulb directly connected to it, and as access to the panel is a lot easier than taking the fan apart, its a good place to start.  However, the fan/lamp wiring has been vibrating due to any slight imbalance in the fan itself, probably for thousands of operating hours if you've been using it much, so is a prime candidate for bad connections.  You'll have to take it down to work on it, so at that point patch in a bulb + holder to its ceiling junction box to eliminate any faults in the circuit up to that point.  It also gives you light in the room so you can take your time to check the fan/lamp assembly thoroughly. 
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Monkeh on October 15, 2016, 04:21:45 am
Is it by any chance a remote controlled fan and light?
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Tomorokoshi on October 15, 2016, 04:35:55 am
Ceiling fans are usually installed sometime after the house was built. In either case, the wiring in the fans is usually somewhat marginal, and the wire nuts supplied with the installation kit are usually on the cheap side.

Check the wire nut connections. Some fan designs have the lamp assembly as a separate unit that screws in underneath the fan motor. There is a space there for the wire nut connections. There is a separate set of wire nut connections in the ceiling box the fan mounts to. This is trickier to service, but the wires can usually be pulled out from the side depending on the support structure without taking the fan off the ceiling.

If the nuts of not sized and used properly the relatively small fan or lamp wire can slip out, particularly of the solid copper 14 or 12 AWG service wiring was not twisted together before the wire nut was put on.

As for Monkeh's point, I've had to replace the remote control receiver assemblies a couple times. I don't recall how they behaved when they failed.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: MK14 on October 15, 2016, 05:17:51 am
This video explains why your specific fan unit flashes like that, and how to fix it.

WARNING:
I'm NOT sure how safe or if it is a good idea, to perform the repair as shown in the video.
Best to get professional/electricians advice or leave it alone.
Video only to help you understand what the problem is (i.e. why it is flashing).

https://www.youtube.com/watch?v=qiBNhKr6JGw (https://www.youtube.com/watch?v=qiBNhKr6JGw)
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Monkeh on October 15, 2016, 05:29:20 am
Oh, yeah, that'd do it.. I'm not sure it's strictly legal to modify it by removing that, but I'd have had it out by now..

You can, apparently, obtain replacements: http://www.ceilingfanremotecontrols.com/fan_limiter_.html (http://www.ceilingfanremotecontrols.com/fan_limiter_.html)

Repair is, I imagine, fairly trivial also.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 15, 2016, 07:20:29 am
Interesting!.    I will try to find out what limiter it has and look for a replacement.

Thank you all!    I'll post the outcome.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Ian.M on October 15, 2016, 07:46:58 am
From the cycling behaviour, the limiter could simply be a self-resetting thermal over-current CB.  If so, if you can get at its contacts and clean them with 600 grit or finer wet&dry paper followed by a strip of thin card wetted with contact cleaner to get any abrasive dust out, it will probably cure it as the usual cyclic failure mode for these is excessive self-heating due to contact burn raising the contact resistance.

I'd also be reluctant to remove it without providing appropriate circuit protection, but alternatively an inline fuse holder with a ceramic slow-blow fuse of an appropriate rating could be used to protect the wiring against idiots overloading the fitting.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: amyk on October 15, 2016, 12:48:58 pm
http://diy.stackexchange.com/questions/1511/what-is-the-purpose-of-a-watt-regulator-in-my-ceiling-fan (http://diy.stackexchange.com/questions/1511/what-is-the-purpose-of-a-watt-regulator-in-my-ceiling-fan)

Regulatory bullshit... along with a touch of planned obolescence |O
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: CatalinaWOW on October 15, 2016, 04:42:10 pm
There is no real safety issue in bypassing the regulator.  Might or might not be a legal issue in your location, but generally no.  All you have to do to keep safe is not put too many watts of lighting in the sockets.  Should be a trivial problem now that LED lights are available.

I have found the replacement regulators hard to find and extremely expensive.  Nearly high enough to justify buying a new low end ceiling fan to salvage the part.  Which is why I have bypassed them in all of the cases I have encountered in being the family handy man.  Three failures out of less than a dozen installations in less than a decade.  Totally unacceptable reliability.

Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Monkeh on October 15, 2016, 04:53:26 pm
I suspect they're very easily repaired. There won't be much to them.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: CatalinaWOW on October 15, 2016, 11:04:06 pm
I thought I should update my comment from above.  The comment reflected my experience about 2011.  Did some quick googling and found that replacement modules are now widely available on the internet (though I still haven't seen them at local hardware stores and the like).  Prices have also come down.  What I found then was going for over $65 as I remember.  Now I found replacement modules available for well under $20.

The hidden message here is that the failure rate has been high enough to quickly create a market for replacements, and that competition in this market has brought prices down.  Not a great message.

I remain unconvinced that these modules provide a safety benefit.  You can easily find reports on line of these modules catastrophically failing, smoke, flames and everything.  But it may be wise to replace them for legal reasons.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: IanB on October 15, 2016, 11:13:42 pm
Replacing them with a wire nut seems like a good idea. But 4 x 40 W bulbs is 160 W -- surely that is enough light for anyone?

In most of my multi-lamp fittings I have replaced the 40 W bulbs with 25 W bulbs. Still plenty bright enough.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Monkeh on October 15, 2016, 11:15:23 pm
They are not for safety reasons - they're designed to limit the power to 190W maximum to comply with energy saving legislation. They'll just be a current-controlled dimmer. Most likely just a cap gone bad inside causing this behaviour.

As I said, I'd just throw the thing away, but that seems to be illegal (modification of a listed fitting).
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 16, 2016, 12:13:37 am
I have removed the lower fan can very easily: three screws and undo a 3x3 wire connector.    The can is really packed!   It contains the rather large limiter, one 3.5uF capacitor, one dual 5uF+5uF capacitor, three switches (lamp, fan, reverse), five wire nuts and a zillion wires.

Peeking inside the limiter through vents it seems to be mostly through hole components.   The exception is a 5x5mm DPAK? with markings T4 1060 7PAAT843, tagged as SCR1 in the PBC.   One MOV disk, couple of resistors, couple of yellow case caps and couple of small electrolytic caps.     

I assume the SCR1 is probably a TRIAC, and since it goes on and off, it is probably ok. 
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Monkeh on October 16, 2016, 12:17:26 am
T410-600 (http://www.st.com/content/ccc/resource/technical/document/datasheet/cf/95/c3/9d/a2/b7/47/43/CD00002383.pdf/files/CD00002383.pdf/_jcr_content/translations/en.CD00002383.pdf)
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Ian.M on October 16, 2016, 01:19:09 am
Odds are replacing the small electrolytics will fix it.   However I wouldn't hesitate to rip it out and fit a fuse - which still meets the requirements of the legislation cited.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 16, 2016, 04:18:37 am
Odds are replacing the small electrolytics will fix it.   However I wouldn't hesitate to rip it out and fit a fuse - which still meets the requirements of the legislation cited.

I will detach it and look at the insides tomorrow.   If I have comparable caps I will replace them.   

Attached a couple of pics
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 17, 2016, 04:47:13 am
I opened the thing.   It does have quite more SMD components under the yellow caps.   I think the electrolytic cap is shot.   Must be very poor quality.   470uF 6.3V, 105.   Brand LM, series GR.   Anybody know what LM is ?

I know I have good 470uF/50V on hand but are too big.   I may have to order some small 10V ones. 
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Monkeh on October 17, 2016, 04:51:42 am
Mmmm, electrolytes. What plants crave.

Bet a 125C cap in that would last a few decades.

A wire would last a few centuries.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Ian.M on October 17, 2016, 05:02:09 am
So patch in your 50V cap and run it open on the bench with a 100W bulb as the load.  If it works you know you are on the right track and can order the right part.  Make sure you get a minimum of a 105 deg C rated cap.

If it doesn't and you cant find any open resistors or shorted diodes etc. then its time to look at scrapping the limiter (maybe trace as much of the circuit as you can and send it to Dave for a teardown?) and patching in an inline fuseholder, which should be a high temperature rated one (usually black or brown phenolic) not a cheap nylon one, with a ceramic body T3A or T3.5A fuse. 
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Bryan on October 17, 2016, 10:10:46 am
Watching some stupid show on the History channel. Ozzy Osborne and his son on some road trip. Ozzy was complaining about his motel room and the lights in a fan flickering off and on. Bet it was the exact same thing.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 17, 2016, 03:57:47 pm
Bet a 125C cap in that would last a few decades.

Unfortunately is not that easy to find a 470uF/6V3/125C in 6.3mm diameter.    The best I have found is 6000hrs at 105C.   Still, probably much better than the LM it would replace.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 17, 2016, 04:01:53 pm
So patch in your 50V cap and run it open on the bench with a 100W bulb as the load.  If it works you know you are on the right track and can order the right part.  Make sure you get a minimum of a 105 deg C rated cap.

Good idea.   I will try that.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: SeanB on October 17, 2016, 05:54:07 pm
Resolder D5 as well, looks like the one leg is cracked in the solder joint.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Back2Volts on October 17, 2016, 07:10:07 pm
Resolder D5 as well, looks like the one leg is cracked in the solder joint.

I guess I will have to unfold the two yellow caps and inspect it all.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Back2Volts on October 17, 2016, 09:33:40 pm
I got the caps out of the way.   It is amazing what an iPhone 5S can do!   Opinions as to what the blue line means ?   
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Monkeh on October 17, 2016, 09:38:41 pm
Programmed, tested, somethingoranother.

That's a Renesas microcontroller.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: IanB on October 18, 2016, 01:38:08 am
I got the caps out of the way.   It is amazing what an iPhone 5S can do!

That capacitor in the picture doesn't look too healthy!
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Monkeh on October 18, 2016, 01:39:17 am
I got the caps out of the way.   It is amazing what an iPhone 5S can do!

That capacitor in the picture doesn't look too healthy!

It followed the instructions of R25 and R27.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: BradC on October 18, 2016, 04:10:19 am
It followed the instructions of R25 and R27.

That was 10 kinds of awesome. Just what I needed this afternoon!
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Monkeh on October 18, 2016, 04:19:04 am
And on a circuit related note.. I have a sneaky suspicion those are biasing the current shunt.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: Back2Volts on October 19, 2016, 04:56:26 pm
So patch in your 50V cap and run it open on the bench with a 100W bulb as the load.  If it works you know you are on the right track and can order the right part.  Make sure you get a minimum of a 105 deg C rated cap.

Done and it fixes the problem  :-+.   

I will order a 6x11mm 105C 5000-6000hrs capacitor.   It is the best I can find in that diameter.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Back2Volts on October 19, 2016, 05:12:31 pm
I assume I will have to remove the white gunk and put new one.   I think I have some of the one used for PC CPUs.

Any ideas to remove the old gunk?  Alcohol ?    The gunk came out pretty well with q tips wet with denat alcohol.
Title: Re: Spontaneous lamp flashing. Absolutely puzzled!
Post by: CatalinaWOW on October 20, 2016, 12:16:07 am
So patch in your 50V cap and run it open on the bench with a 100W bulb as the load.  If it works you know you are on the right track and can order the right part.  Make sure you get a minimum of a 105 deg C rated cap.

Done and it fixes the problem  :-+.   

I will order a 6x11mm 105C 5000-6000hrs capacitor.   It is the best I can find in that diameter.

Good diagnosis and fix.  It is just sad that after doing this you just have a lamp that forces you not to do something stupid, something that requires real effort to do wrong.  And does so at with higher initial cost and significantly lower reliability.  I would be far more in support of this device if it had just a little more functionality added that is useful to the owner.  It is ninety percent of the way to a built in dimmer. Or better yet a dimmer that maintains a constant light level in a room as natural light level changes.  Or something else that has more positive value.
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: Back2Volts on November 16, 2016, 02:21:43 pm
I finally got around ordering batch of components from Newark.   Soldered the new capacitor in and assembled it back in the fan.
It is working great.

Thank you guys for the support   
Title: Re: Spontaneous lamp flashing. Hunter fan limiter failure
Post by: MK14 on November 16, 2016, 02:54:26 pm
I finally got around ordering batch of components from Newark.   Soldered the new capacitor in and assembled it back in the fan.
It is working great.

Thank you guys for the support