Stange Problem with GFCI
« on: April 15, 2014, 03:04:55 pm »
I am not an expert on GFCI, but I do know how they work, however I have had a strange problem in my lab with one in particular that keeps nuisance tripping. Here is the scenario, I have one part of the lab which uses a computer and about 8 to 12 low powered devices which not all on at the same time. They are fed from a 20A circuit to the GFCI and (2) standard outlets are supplied by the "LOAD" side of the GFCI for a total of (3) outlets. Equipment has been running for a few years on this setup with no problems until recently I started to get tripping of the GFCI several times a day. Now, here is where it gets weird, I have monitored the power coming into the GFCI and it appears to be good. I have checked for leakage current which is in the range of less than a few mA. The GFCI should not trip until at least 5mA> from what I know. This problem has never occurred at night, only in the middle of the day and not instantly when equipment is used. I can do all the same activity on the equipment in the evening with no issues at all. I check the power feed coming into the lab with an RFI line meter and get around 150mV or less of HF noise which is not bad considering I have seen upwards of 400-500 mV in new building installations. I have unplugged equipment, tried various combinations and cannot seem to isolate this problem. The current draw is maybe 2 amps at best and averages around 600mA to 1.2A. Since GFCI is not effected by current draw I don't think this is the problem. I guess it could be a bad GFCI, it's not to terribly old though. Their is an APC UPS on one of the "LOAD" outlets but it has been running for over 6 months now without issue.

Any recommendations to try before I pull this GFCI and try a new one, or even replace it with a standard outlet?

Eric Haney, MCSE, EE, DMC-D
Electronics Designer, Prototype Builder
 

Offline ajb

  • Super Contributor
  • ***
  • Posts: 2759
  • Country: us
Re: Stange Problem with GFCI
« Reply #1 on: April 15, 2014, 03:51:58 pm »
Are there significant temperature/humidity fluctuations between the daytimes and evenings?

Probably the most informative troubleshooting step would be to replace the GFCI, and if the problem persists it's a good indication that the problem is a result of the setup or environment rather than just a faulty/worn out GFCI.
 

Offline Terabyte2007Topic starter

  • Frequent Contributor
  • **
  • Posts: 527
  • Country: us
  • It is purpose that created us... That defines us..
Re: Stange Problem with GFCI
« Reply #2 on: April 15, 2014, 03:55:54 pm »
Are there significant temperature/humidity fluctuations between the daytimes and evenings?

Probably the most informative troubleshooting step would be to replace the GFCI, and if the problem persists it's a good indication that the problem is a result of the setup or environment rather than just a faulty/worn out GFCI.

No, the temp/humidity is regulated and it stays pretty close to the same day and night.

I was trying to avoid swapping it if I could, but that may be my only option soon.
Eric Haney, MCSE, EE, DMC-D
Electronics Designer, Prototype Builder
 

Offline SeanB

  • Super Contributor
  • ***
  • Posts: 16384
  • Country: za
Re: Stange Problem with GFCI
« Reply #3 on: April 15, 2014, 07:20:15 pm »
Probably leakage current has increased in something, along with a failing GFCI which is getting more sensitive to noise. Easiest is to replace it, they are cheap enough. Better is to give each outlet it's own GFCI controlled circuit, that way the ground currents do not add up to a trip level.

I have had that issue as well with 20 SMPS units on a circuit that tripped at random times. Solved by adding a second GFCI and splitting the circuit into 2 parts each of which did half.
 

Offline Richard Crowley

  • Super Contributor
  • ***
  • Posts: 4321
  • Country: us
  • KJ7YLK
Re: Stange Problem with GFCI
« Reply #4 on: April 15, 2014, 07:38:29 pm »
GFCI devices are relatively precision, but MASS produced commodity items.  And they are likely designed to "fail" safely. Which means that they may interrupt where they don't need to vs. the other option (to NOT interrupt where they should).

So just replace it. They aren't that expensive, and they weren't made to last forever.  When you get the old one out, do a tear-down video for us. I didn't find anything about "GFCI" when I searched the eevblog website.
 

Offline SeanB

  • Super Contributor
  • ***
  • Posts: 16384
  • Country: za
Re: Stange Problem with GFCI
« Reply #5 on: April 15, 2014, 08:01:35 pm »
I think I should take an old 1960's technology one apart then, they actually have electronics inside like a BRY39 switch.
 

Offline 128er

  • Regular Contributor
  • *
  • Posts: 229
  • Country: de
Re: Stange Problem with GFCI
« Reply #6 on: April 15, 2014, 08:02:36 pm »
First, a question ...

Do we talk about, what I know as a "RCD", residual current device?  All three, or only 1 phase and the neutral pass through a "summation transformer", the magnetic fields cancel each other out and there is no induction to trip the mechanism.

The differential current of your device is 5mA? fairly low, I think
How do you measured the leakage and where? If you have a current clamp, put the neutral and the phase in the clamp. There should be no current.
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #7 on: April 15, 2014, 08:03:52 pm »
Do we talk about, what I know as a "RCD", residual current device?  All three, or only 1 phase and the neutral pass through a "summation transformer", the magnetic fields cancel each other out and there is no induction to trip the mechanism.

Yes.

Quote
The differential current of your device is 5mA? fairly low, I think

Normal in Yankistan.
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 8221
  • Country: de
  • A qualified hobbyist ;)
Re: Stange Problem with GFCI
« Reply #8 on: April 15, 2014, 08:14:06 pm »
I have had that issue as well with 20 SMPS units on a circuit that tripped at random times. Solved by adding a second GFCI and splitting the circuit into 2 parts each of which did half.

The current through the Y filter caps adds up with each SMPS. The 5mA of the RCD could be easily exceeded. Therefore we got local restrictions for the max value of the Y caps to limit the current per device (30mA RCDs are standard).
 

Offline 128er

  • Regular Contributor
  • *
  • Posts: 229
  • Country: de
Re: Stange Problem with GFCI
« Reply #9 on: April 15, 2014, 08:19:16 pm »


Quote
The differential current of your device is 5mA? fairly low, I think

Normal in Yankistan.

Ok, here in germany it is 30mA for circuits with sockets up to 32 Amps, that are accessible for electrical laymans (almost everyone). Lesser in medical enviorments for example. But the RCD's are allowed to trip at about 50% of the rated differential current. Most of them trip between 20-30 mA.

Edit:
madires is quite right about that
« Last Edit: April 15, 2014, 08:20:58 pm by 128er »
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #10 on: April 15, 2014, 08:20:10 pm »


Quote
The differential current of your device is 5mA? fairly low, I think

Normal in Yankistan.

Ok, here in germany it is 30mA for circuits with sockets up to 32 Amps, that are accessible for electrical laymans (almost everyone). Lesser in medical enviorments for example. But the RCD's are allowed to trip at about 50% of the rated differential current. Most of them trip between 20-30 mA.

They don't protect circuits in the US, they protect outlets.
 

Offline 128er

  • Regular Contributor
  • *
  • Posts: 229
  • Country: de
Re: Stange Problem with GFCI
« Reply #11 on: April 15, 2014, 08:27:57 pm »


They don't protect circuits in the US, they protect outlets.

With circuits i meant outlets. The RCD sits in the distribution board and protect the outlet. (Find the right term in english is not easy :D )
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #12 on: April 15, 2014, 08:30:14 pm »


They don't protect circuits in the US, they protect outlets.

With circuits i meant outlets. The RCD sits in the distribution board and protect the outlet. (Find the right term in english is not easy :D )

Yes, I know what you meant. They don't do that in the US, they build the RCCB into the outlets.
 

Offline Richard Crowley

  • Super Contributor
  • ***
  • Posts: 4321
  • Country: us
  • KJ7YLK
Re: Stange Problem with GFCI
« Reply #13 on: April 15, 2014, 08:31:50 pm »
They don't protect circuits in the US, they protect outlets.
Actually, there are GFCI breakers available to protect the entire circuit. They install just like regular breakers, but they implement the GFCI (or RCD) function by separate connection to the neutral bus for reference.

 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #14 on: April 15, 2014, 08:33:55 pm »
They don't protect circuits in the US, they protect outlets.
Actually, there are GFCI breakers available to protect the entire circuit.

And how often do you see those used? It is, from everything I've seen, not standard practice (like a great many other things..).

Not to mention protecting an entire circuit with a 5mA device would be lunacy.

Proper IEC 60898-1 and 60947-2 breakers are available in the US, too, but you don't use them in distribution.
« Last Edit: April 15, 2014, 08:36:54 pm by Monkeh »
 

Offline Richard Crowley

  • Super Contributor
  • ***
  • Posts: 4321
  • Country: us
  • KJ7YLK
Re: Stange Problem with GFCI
« Reply #15 on: April 15, 2014, 08:36:38 pm »
Well, perhaps you don't see many there in the UK.  But here in the US, I have seen many of them. And I believe they are now legally required for kitchen, bath, laundry, and exterior circuits.
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #16 on: April 15, 2014, 08:37:45 pm »
Well, perhaps you don't see many there in the UK.  But here in the US, I have seen many of them.

What we have here is a failure to communicate.
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 8221
  • Country: de
  • A qualified hobbyist ;)
Re: Stange Problem with GFCI
« Reply #17 on: April 15, 2014, 09:00:37 pm »
Well, perhaps you don't see many there in the UK.  But here in the US, I have seen many of them. And I believe they are now legally required for kitchen, bath, laundry, and exterior circuits.

We've had that requirement for over 20 years. Nowadays the whole apartment needs to be protected by RCDs in the distribution panel. And you should install several ones to prevent a complete lights-off in the night and to deal with high load areas like a kitchen. Typical RCDs used are 3-phase 25, 40 and 63A (trip at 30mA max).
 

Offline Terabyte2007Topic starter

  • Frequent Contributor
  • **
  • Posts: 527
  • Country: us
  • It is purpose that created us... That defines us..
Re: Stange Problem with GFCI
« Reply #18 on: April 15, 2014, 09:01:28 pm »
Probably leakage current has increased in something, along with a failing GFCI which is getting more sensitive to noise. Easiest is to replace it, they are cheap enough. Better is to give each outlet it's own GFCI controlled circuit, that way the ground currents do not add up to a trip level.

I have had that issue as well with 20 SMPS units on a circuit that tripped at random times. Solved by adding a second GFCI and splitting the circuit into 2 parts each of which did half.

I suspected something along these lines so I did a bit more troubleshooting today and found a Cheap Chinese Switch-Mode power wall wart to be likely putting the edge on the leakage current. It was a 2A/12V for a 20 dollar SATA drive caddy. When I plugged this PS in within 1-15 minutes it would trip. I don't think it was causing it by itself, but an additive effect with all the devices connected to the circuit. This just kinda put it over the edge.
Eric Haney, MCSE, EE, DMC-D
Electronics Designer, Prototype Builder
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #19 on: April 15, 2014, 09:02:31 pm »
Probably leakage current has increased in something, along with a failing GFCI which is getting more sensitive to noise. Easiest is to replace it, they are cheap enough. Better is to give each outlet it's own GFCI controlled circuit, that way the ground currents do not add up to a trip level.

I have had that issue as well with 20 SMPS units on a circuit that tripped at random times. Solved by adding a second GFCI and splitting the circuit into 2 parts each of which did half.

I suspected something along these lines so I did a bit more troubleshooting today and found a Cheap Chinese Switch-Mode power wall wart to be likely putting the edge on the leakage current. It was a 2A/12V for a 20 dollar SATA drive caddy. When I plugged this PS in within 1-15 minutes it would trip. I don't think it was causing it by itself, but an additive effect with all the devices connected to the circuit. This just kinda put it over the edge.

And this, folks, is why 5mA RCCBs are stupid.
 

Offline Terabyte2007Topic starter

  • Frequent Contributor
  • **
  • Posts: 527
  • Country: us
  • It is purpose that created us... That defines us..
Re: Stange Problem with GFCI
« Reply #20 on: April 15, 2014, 09:02:45 pm »
GFCI devices are relatively precision, but MASS produced commodity items.  And they are likely designed to "fail" safely. Which means that they may interrupt where they don't need to vs. the other option (to NOT interrupt where they should).

So just replace it. They aren't that expensive, and they weren't made to last forever.  When you get the old one out, do a tear-down video for us. I didn't find anything about "GFCI" when I searched the eevblog website.

That sounds like a good idea, I will do so.
Eric Haney, MCSE, EE, DMC-D
Electronics Designer, Prototype Builder
 

Offline denelec

  • Regular Contributor
  • *
  • Posts: 168
  • Country: ca
Re: Stange Problem with GFCI
« Reply #21 on: April 15, 2014, 11:49:38 pm »
I've read that RCD were initially used in Europe to prevent electricity theft.
Because a load wired phase to ground instead of phase to neutral wouldn't be seen by the meter.
Can anybody confirm this?
In US and Canada, the meter is not referenced to ground.  It only sees the 240V (line-line) and the two line currents.
A phase to ground load will be measured.
GFCI are used only to prevent electrical shock.
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #22 on: April 15, 2014, 11:52:19 pm »
I've read that RCD were initially used in Europe to prevent electricity theft.
Because a load wired phase to ground instead of phase to neutral wouldn't be seen by the meter.
Can anybody confirm this?

Load of crap. That's not how meters work or where RCDs are fitted.
 

Offline denelec

  • Regular Contributor
  • *
  • Posts: 168
  • Country: ca
Re: Stange Problem with GFCI
« Reply #23 on: April 16, 2014, 12:14:56 am »
I've read that RCD were initially used in Europe to prevent electricity theft.
Because a load wired phase to ground instead of phase to neutral wouldn't be seen by the meter.
Can anybody confirm this?

Load of crap. That's not how meters work or where RCDs are fitted.

This document from ABB seems to confirm the electricity theft theory:
http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/c4e584f06cc6c4fbc1257ad800496193/$file/2CSC420004B0201_RCDs%20EN.pdf
See page 7 of the document: "It is not clear when and by whom the first RCD was developed, but it certainly appeared on the
market in the 1950s and was initially used by some utility companies to fight “energy theft” due
to the use of currents from phase to earth instead of phase to neutral.
"

So maybe I'm not so "full of it" somehow... ;)
 

Online Monkeh

  • Super Contributor
  • ***
  • Posts: 8102
  • Country: gb
Re: Stange Problem with GFCI
« Reply #24 on: April 16, 2014, 12:21:10 am »
I've read that RCD were initially used in Europe to prevent electricity theft.
Because a load wired phase to ground instead of phase to neutral wouldn't be seen by the meter.
Can anybody confirm this?

Load of crap. That's not how meters work or where RCDs are fitted.

This document from ABB seems to confirm the electricity theft theory:
http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/c4e584f06cc6c4fbc1257ad800496193/$file/2CSC420004B0201_RCDs%20EN.pdf
See page 7 of the document: "It is not clear when and by whom the first RCD was developed, but it certainly appeared on the
market in the 1950s and was initially used by some utility companies to fight “energy theft” due
to the use of currents from phase to earth instead of phase to neutral.
"

So maybe I'm not so "full of it" somehow... ;)

I've never seen a meter with anything but a solid link for a neutral, so I'd love to know how that's meant to work..
 