Be careful here, what is the meter that your using to make these measurements, depending on the meter, those kind of voltages, especially in free air are understandable and may well be normal. I was going down the line of the high impedance on the LED's and or driver which if there was a leakage, charge up the capacitor sufficient to cause the LEDs to flash, discharge the cap and then the cycle repeats. Have you checked the resistance between the ground connection on the fitting and the neutral and also the ground and live? I believe that is more likely to slight tracking from ground to either the neutral or the live at the fitting and a bad earth connection somewhere along the line to the mail earth point.
Most likely is a build up of the leakage to ground of the various filter capacitors on many items these days could well be dumping a fair amount of mA to ground and if the main ground connection, be it a rod in the ground or the sheathing of your incoming supply
EDIT
I just did a test using my Brymen BM867 sitting here at my bench I can get 80mV AC with both the leads in free air, if I touch either of the probes this raises to 830 mV and the same if I connect with neutral so as I was saying earlier, those voltages are to be expected