Author Topic: Why Circuit Breakers DON'T Protect People (electric shocks)  (Read 6050 times)
Offline JoeRoyTopic starter
« on: April 21, 2024, 01:23:49 am »
Re: Why Circuit Breakers DON'T Protect People (electric shocks)
« Reply #1 on: April 21, 2024, 07:45:35 am »
Errm, because they aren't intended to? Circuit breakers are intended to prevent the wiring from becoming a fire hazard, nothing more.
GFCI/RCD/RCBO are the devices intended to protect people.
The following users thanked this post: ebastler, tooki, Gregg, newbrain, nvmR
Offline Gyro
It's quite a good video description and operational demonstration of the internals of an MCB. Of course the MCB is a an overcurrent device (replacing the older consumer unit fuses) and has nothing to do with shock protection. The video does show the internals of a UK split-load consumer unit and shows the RCDs in place, but doesn't describe their role in protecting against current leakage and shock.
There must be another video in the series that describes the purpose and operation of RCDs.
EDIT: In fact he describes it in this video...
Maybe he will go on to produce a video of the RCD internals at some point. Most new UK installations now include RCBOs, which combine the function of MCB and RCD on each individual circuit.
« Last Edit: April 21, 2024, 10:41:18 am by Gyro »
Best Regards, Chris
Offline Zero999
  • 0999
« Reply #3 on: April 21, 2024, 10:55:46 am »
I don't have time to watch those videos.
It's not completely true. Before the advent of RCDs and RCBOs, circuit breakers and fuses certainly did some provide protection against electric shock. When the line conductor makes contact with a a piece of equipment's earthed case, the over current protection device has to quickly interrupt the current in order to keep the voltage on the exposed metalwork form reaching a hazardous voltage. If there's no RCD and inadequate over current protection, then it's possible for exposed, earthed contactors to reach a hazardous voltage, under fault conditions.
Nowadays, RCDs and RCBOs provide protection against shock from earth leakage, so the role of over-current protection is mostly to prevent fire, but it's still good to have another layer of shock protection.
The following users thanked this post: tom66, Someone, newbrain, SiliconWizard
Online EPAIII
« Reply #4 on: April 26, 2024, 07:02:45 am »
Ah, but by preventing fires,
THEY DO PROTECT PEOPLE.
Paul A.  -   SE Texas
And if you look REAL close at an analog signal,
You will find that it has discrete steps.
The following users thanked this post: BlownUpCapacitor
Offline tom66
« Reply #5 on: April 26, 2024, 01:34:03 pm »
RCDs also prevent fires.  One of the original justifications for RCDs was detecting rodent damage to tasty cables.  A rodent could chew through a cable and create a path from live to earth which might be insufficient to trigger an MCB but the imbalance would quickly trip an RCD.
This is a particular issue in lofts.
https://www.electrical-installation.org/enwiki/Protection_against_fire_due_to_earth_faults
« Reply #6 on: April 26, 2024, 02:21:55 pm »
Yeah, take that article with a pinch of salt; it's by Schneider Electric.
Offline mendip_discovery
« Reply #7 on: April 26, 2024, 03:55:56 pm »
Why does everything HAVE to be a video these days, and then damned lazy posting it to a group.
Anyway, as someone who has taken a few 230V AC shocks and even one rather bracing belt with a few kV. The time you are exposed does make a difference. 10 ms compared to ∞ (or how long before the power is cut) is often the difference between walking away or not.
Motorcyclist, Nerd, and I work in a Calibration Lab :-)
So everyone is clear, Calibration = Taking Measurement against a known source, Verification = Checking Calibration against Specification, Adjustment = Adjusting the unit to be within specifications.
Offline Gyro
« Reply #8 on: April 26, 2024, 07:22:50 pm »
Better that than Hager.  ;)
Best Regards, Chris
« Reply #9 on: April 27, 2024, 03:50:07 pm »
I wouldn't trust any manufacturer to not try to use the opportunity to sell you their product.
Online Andy Chee
« Reply #10 on: April 28, 2024, 05:39:20 am »
If the electric current is enough to contract your muscles and grip that live wire with even greater strength, of course the exposure time is only going to increase.
