This is why proper 'clouds' have availability regions and availability zone. Most cloud providers don't promise 100% availability - it's the customer's responsibility to architect their systems correctly for the availability and redundancy they need.
Gaseous fire suppression are not really practical in 'warehouse scale' data centers.... when triggered the rise in air pressure can literally blow the roof off or walls out, and the systems themselves present a risk (lots of gas in high pressure cylinders). Nor is localized inert gas fire suppression effective in Data Centers as they often don't have confined spaces and the have lots of fans and chillers moving air around to cool the equipment.
In a lot of cases it's good site practices (e.g. no cardboard/paper, good cable management, hotwork processes, regular inspection with IR cameras), VESDA, temperature monitoring, and finally well-trained people with fire extinguishers as the last line of defense.
Sure, you can engineer up to it, but having a workable BCP costs less.