Is  digital electricity a thing now ?  I saw this video on a company named  3DFS (https://3dfs.com/)  that  claims they can save you 70%  power on the electric  grid  is this  true. This  product claims to analysis the input power and  in real time clean up all the harmonics and distortions and  create a perfect  sin wave out put.  it seems to me  it  really claiming to be a power factor correction device but  savings look  over blown.  another video
Online Ian.M
Re: digital electricity
« Reply #1 on: June 06, 2018, 07:01:01 am »
You don't even need to watch the video to know that a claim of 70% savings is pure platinum plated bulls--t and any device that claims to provide it is pure snake oil.
Start with the Laws of Thermodynamics which tell you that energy cant be created from nothing, and that all lost energy must eventually end up as waste heat.
Therefore that claimed 70% saving must mean that on average, your electrical appliances have an efficiency below 30%.   However most modern PSUs have efficiency over 80%, and air heating appliances  can have efficiencies up to 100% - as the 'waste' heat is the desired result, so unless you have a house full of valve amps or similar there isn't enough lost energy 'on the table' to get anywhere near a 70% saving.
Then there's the results of waveform distortion on efficiency.  The most common waveform distortion - 'flat topping' caused by SMPSUs without power factor correction (PFC) drawing all their current at the peaks of the mains waveform actually increases the efficiency of other SMPSUs as it widens the effective peak so decreases I2R losses in the wiring, input filter and bridge rectifier feeding the input side DC bus, and in the PFC circuit if present.  Therefore claims of general efficiency savings by improving power quality have a fishy smell to start with - like last weeks fish guts left out in the sun!
When all's said and done if you could magically clean up the mains waveform without loosing any energy, I'd be *extremely* surprised to see even a 1% improvement in efficiency, and if the device actually does anything, it will be subject to the same constraints on losses as any other electrical or electronic device, so its likely that its losses will be a few percent of the load on it, wiping out any potential saving immediately.
Its true that way back in the day,many industrial and large commercial power users could make large savings by installing power factor correction capacitors, as traditionally commercial and industrial loads were typically largely inductive (think big motors and choke ballasted fluorescent lighting), and the tarrifs they were on often penalised power factors that were too low (excessive VAR) but nowadays there are very few inductive domestic loads that run for longer than a few minutes, and to meet national energy efficiency targets, most inductive loads will already have power factor correction components internally fitted.  Also domestic metering only measures real power, it doesn't measure VAR, so as you aren't on a tarrif + metering that penalises peak VAR the only saving to the user is reduced I2R losses in the wiring between the power factor correction device and the meter.  All I2R losses upstream of the meter come out of the power company's operating overheads so savings in the distribution network wont save the end users a single cent (though they'll probably make shareholders happy).
« Last Edit: June 06, 2018, 07:06:06 am by Ian.M »
Offline cdoerfler
    • 3DFS Software-Defined Electricity
-Cofounder of 3DFS Software-Defined Electricity & SAM Controllers
The following users thanked this post: thefinisher
Offline niladherbert
« Reply #3 on: June 06, 2018, 02:45:50 pm »
The company is really selling a nice way of cleaning up your power into a perfect sine wave, while claiming all sorts of things about it, but it would give marginal gains in efficiency (like the capacitor in a box teardown). The cub on the video needs an education on AC and DC, P=IV and V=IR. He also needs told that only as much current as the device needs to consume is drawn. He really hasn't done his research on how the grid is controlled though.
Just read that article. Here's a real gold nugget: “Smart meters are a few hundred bucks because they do not have processors inside them". I don't see how they can help on reasonably well built DC power regulation within normal electronics like they're talking about at the end though. And they're 'Not in it for the money as much as the improvements to society'
Offline JohnnyMalaria
    • Enlighten Scientific LLC
« Reply #4 on: June 06, 2018, 03:39:20 pm »
Look at the size of the two fans on that thing. They'd barely fit in the microwave. Must generate a lot of heat trying to stop your appliances generating heat.  :-// :palm: :scared: :bullshit:
Tell me it can't be done and I'll do it. Or give it a damned good try.
Offline cdoerfler
« Reply #5 on: June 06, 2018, 04:12:32 pm »
This device consumes a maximum of 120Watts of power all time. Those fans only turn on when the device must prevent a lightning surge from entering the panel.
« Reply #6 on: June 06, 2018, 04:51:39 pm »
Aren't lightning surges very short (<0.5ms)? How can the fans possible come on that fast and do anything to help?
Do you have a full technical specification sheet? Your website is very vague about power draw etc.
Offline cdoerfler
« Reply #7 on: June 06, 2018, 05:17:29 pm »
They are very short, but the heating is delayed and the power is absorbed.  The fans turn on at the sensing of the surge and continue until the ambient temperature returns. The inductive system is also water cooled and oil cooled, which further assists in rapid cooling. Spec sheet attached.
Offline james_s
« Reply #8 on: June 06, 2018, 06:34:06 pm »
 :popcorn:
Offline StillTrying
  • Country: Broken Britain
« Reply #9 on: June 06, 2018, 08:31:08 pm »
There's plenty of more 'info' out there, if anyone needs a laugh.
www.you  tube.com/watch?v=2m5nJ1gkOHI
www.you  tube.com/watch?v=8x4r8-OoFG4
www.you  tube.com/watch?v=omkc6MkS17U
« Last Edit: June 06, 2018, 08:32:56 pm by StillTrying »
CML+  That took much longer than I thought it would.
Offline Circlotron
« Reply #10 on: June 06, 2018, 10:06:09 pm »
As Clara Clayton said to Doc Emmet Brown, “I’ve heard some whoppers I’m my time...”
Offline cdoerfler
« Reply #11 on: June 06, 2018, 11:01:57 pm »
Here I am to engage you in a dialogue about this technology and this is what I get. I thought there were "experts" on this forum. I thought there were knowledgeable people who could contribute to the conversation and might even learn a thing or two.
Instead, this...
Good job guys!
« Reply #12 on: June 06, 2018, 11:23:22 pm »
So, if I understand it, your device monitors the phase difference between the voltage and the current at any given moment and this can change either due to the grid or an appliance (esp. high power) causing it.
How can your device introduce a phase difference between what's coming in to the panel and what's going to the appliances etc at high load (30A say) with such small wires? Otherwise won't the phase difference in the building simply be the same as what's coming in?
To change the phase requires energy. Using P = VI cos(phase) and let's say the undesirable phase is -10deg then the power will change from VI cos(-10deg) to VI cos(0) which is about VI x 0.02. 30A equates to 115V x 30A = 3.45kW. 0.02 of that is 69W. So, assuming 100% efficiency, somewhere you have to find 69W of energy or dissipate it (can't think that through right now) but you spec says that the idle power consumption is 90W or so and the max is 120W. That's only 30W difference and I'm sure it isn't 100% efficient. So how are you changing the phase?
And a phase shift of 10deg (the range of your device) only creates a loss of 2% power which wouldn't be that significant in a house as far as the bill is concerned. How quickly would someone break even with the cost of the device and the utility bill saving?
I'm missing something.
Offline StillTrying
« Reply #13 on: June 06, 2018, 11:24:46 pm »
I thought everyone knew that we're all moving over to the new Natively Digital Format square wave electricity now, it's much more convenient, efficient and safer than the now old fashioned analogue sine wave AC.
www.digitizelectric.com/how-it-works
www.voltserver.com
Offline cdoerfler
« Reply #14 on: June 06, 2018, 11:58:50 pm »
It sounds like you are inquiring about the power electronics. How do we perform the correction?
The technology has an inductive system and a capacitive system in the box. We call it a Flash Energy Storage System or FESS for simplicity of reference where energy is only temporarily stored (no longer than a microsecond).
Each microsecond, there is a correction made to the by either charging or discharging our FESS depending on the inductive or capacitive need of the power network in the moment. This correction is always precise and accurate, based on the Real-Time computing analysis that occurs in between each correction.
The result is the power network impedance is always matched to the Real-Time need of the collective power consumption of all the loads. This is the live nature of our technology. It does not matter how the loads are consuming electricity, the supply is adjusted to meet the demand.
When the impedance is automatically matched, every load in the panel receives the precise, perfect power that it demands immediately reducing energy consumption and improving the device performance.
« Reply #15 on: June 07, 2018, 12:11:49 am »
So every device is optimized independently?
Offline thefinisher
  • Country: tt
« Reply #16 on: June 07, 2018, 12:14:02 am »
That what was my thinking that it was doing some form of power fact correction at best but using a form of intelligent microcontroller to regulate and adjust the phase difference between the voltage and the current. I did not think any microcontroller would be fast enough to do this in real time to make this phase changes and harmonic adjustment in real time.
« Reply #17 on: June 07, 2018, 12:15:31 am »
Offline james_s
« Reply #18 on: June 07, 2018, 12:18:27 am »
Why would it matter anyway? At least in the US, residential customers are not billed based on power factor, so while a perfect unity power factor is desirable and will result in a very slight reduction in cable losses, it's not something that is going to have a measurable effect on the bill.
Offline Euler
« Reply #19 on: June 07, 2018, 12:19:50 am »
www.voltserver.com
Seriously StillTryin, Do really you not know the difference between AC and DC ???  You clearly have not been burdened by an overabundance of education.
« Last Edit: June 07, 2018, 12:21:25 am by Euler »
Offline cdoerfler
« Reply #20 on: June 07, 2018, 12:55:39 am »
It is a different perspective. The electricity is optimized to deliver perfect power to the loads.
« Last Edit: June 07, 2018, 01:04:34 am by cdoerfler »
Offline cdoerfler
« Reply #21 on: June 07, 2018, 12:57:00 am »
Yeah, this is difficult. The core innovation behind this is Real-Time computing. This device has the ability to process terabytes of data every minute at the expense of 120W of power. This is the huge achievement that allows for this to occur in Real-Time.
« Last Edit: June 07, 2018, 01:04:57 am by cdoerfler »
Offline cdoerfler
« Reply #22 on: June 07, 2018, 01:02:16 am »
This is partially true. Power factor penalties are not directly charged to residential consumers in most markets, but they are a significant charge for commercial and industrial customers.
From an energy efficiency standpoint it is not just power factor, it is harmonics and the imbalance between the phases that cause additional waste, and they all induce further waste among each other. This multiplication effect of losses wastes energy and results in poor power to every single load in the power network all the time.
This underperformance of devices is directly linked to waste in manufacturing and production and is linked to poor data transfer between servers and under performance in UPS, etc.
Synchronized electricity is energy efficiency and process improvement all at once. This has enormous effects on some industries like semi-conductor fabs or pharmaceutical research, etc.
« Last Edit: June 07, 2018, 01:05:14 am by cdoerfler »
Offline cdoerfler
Offline thefinisher
  • Country: tt
« Reply #24 on: June 07, 2018, 01:40:22 am »
I have some  questions about the technology how does it harmonic cause energy lost what is the mathematics behind this
The following users thanked this post: rs20, golden_labels