Are they all on the same supply, single phase, or 3 phase? If so, and they are all fused with a single block of overcurrent protection, and are the same manufacturer and model, then look into connecting the DC bus inside each of them with a commoning DC bus, and add in a brake resistor as well to this common bus. Rating of brake resistor is that of the largest supply. this will also allow energy recovery from motors stopping, with this being used by the other inverters, or, if too large, in the brake resistor to dump the energy safely. Very easy to do and also a big saving in energy, plus any emergency stop operation, that disconnects power input, will result in all drives shutting down safely, and not having an overvolt trip out as they brake the motors to a stop. typically you have a large VDFD, and a few smaller ones, so the large one operates most of the time, and the small ones stop and start as needed, but having the DC bus commoning means you can go for much faster speed change rates, as the individual inverters wheel power amongst them, and can ramp down to stop from full speed in as little as a single revolution, and not have an overvolt or overcurrent trip, even doing it multiple times a minute. Seen that in a big motor control station, where the main motors were 100kVA variable speed drives on hydraulic pumps, and the small motors were 22kVA motors running at a ramp up from zero to 100Hx in a half turn, and the same back down. Had nearly 1F of DC bus capacitor, at 800VDC, and a brake chopper that was a separate cabinet above it, connected with a massive bundle of cables that allowed the controller to vary the dump power smoothly, and a set of 10 115mm fans running all the time to cool them. 40mm power cables to feed it, and it was 40 tons for the controller cabinet alone.
If they are separate drives contact the local supplier, and get individual brake chopper modules for each drive, one per drive, sized for the drive power. As well, if the drives are on a very stiff supply (short circuit power capacity exceeding 10kA) you probably want to get some line reactor chokes on the incoming supply per inverter as well.