Author Topic: AC to DC voltage mirror for reference?  (Read 962 times)

0 Members and 1 Guest are viewing this topic.

Offline pacmannTopic starter

  • Contributor
  • Posts: 36
  • Country: jp
AC to DC voltage mirror for reference?
« on: August 06, 2021, 07:32:28 am »
Whats the best way to convert an AC voltage to its equivalent DC for measurement? The output can be low current in the 10-50 mA range.

As an example, if there is 200 vpp AC I want to create a 200 vdc reference voltage. Does this kind of circuit have a name?
 

Offline pacmannTopic starter

  • Contributor
  • Posts: 36
  • Country: jp
Re: AC to DC voltage mirror for reference?
« Reply #1 on: August 06, 2021, 09:22:37 am »
Can the circuit be as easy as a bridge rectifier with parallel capacitor?
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19962
  • Country: gb
  • 0999
Re: AC to DC voltage mirror for reference?
« Reply #2 on: August 06, 2021, 09:59:57 am »
It depends on whether the voltage drop across the rectifier diodes is a problem or not. Under light loads, a silicon diode will typically drop around 0.6V and they're two in series in a bridge rectifier giving a total drop of 1.2V.

Another thing to note is AC voltages are normally specified by the RMS (Root Mean Square) voltage. A rectifier and filtering capacitor will give you the peak voltage, which is higher by a factor of √2, so 200VAC RMS in, will give 200√2 = 283VDC out, minus the diode voltage drops.
 
The following users thanked this post: pacmann

Offline pacmannTopic starter

  • Contributor
  • Posts: 36
  • Country: jp
Re: AC to DC voltage mirror for reference?
« Reply #3 on: August 06, 2021, 10:45:38 am »
It depends on whether the voltage drop across the rectifier diodes is a problem or not. Under light loads, a silicon diode will typically drop around 0.6V and they're two in series in a bridge rectifier giving a total drop of 1.2V.

Another thing to note is AC voltages are normally specified by the RMS (Root Mean Square) voltage. A rectifier and filtering capacitor will give you the peak voltage, which is higher by a factor of √2, so 200VAC RMS in, will give 200√2 = 283VDC out, minus the diode voltage drops.
Thanks for explaining. I think the drop of 1.2v will be ok.

Can the RMS be compensated with someting like a resistor divider at the DC side? Is there a better way than a divider?

Is there a way to isolate the input without using a transformer because of the low output current requirement?
« Last Edit: August 06, 2021, 10:59:43 am by pacmann »
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19962
  • Country: gb
  • 0999
Re: AC to DC voltage mirror for reference?
« Reply #4 on: August 06, 2021, 11:14:27 am »
It depends on whether the voltage drop across the rectifier diodes is a problem or not. Under light loads, a silicon diode will typically drop around 0.6V and they're two in series in a bridge rectifier giving a total drop of 1.2V.

Another thing to note is AC voltages are normally specified by the RMS (Root Mean Square) voltage. A rectifier and filtering capacitor will give you the peak voltage, which is higher by a factor of √2, so 200VAC RMS in, will give 200√2 = 283VDC out, minus the diode voltage drops.
Thanks for explaining. I think the drop of 1.2v will be ok.

Can the RMS be compensated with someting like a resistor divider at the DC side? Is there a better way than a divider?

Is there a way to isolate the input without using a transformer because of the low output current requirement?
If the AC signal is always a sine wave, then a potential divider can be used to divide by √2.

An analogue isolator can be used to isolate the signal, but the usual way is to digitise the signal first and pass it through a digital isolator. It's also possible to use PWM, or PFM the signal before passing it through a digital isolator.
 

Offline fcb

  • Super Contributor
  • ***
  • Posts: 2130
  • Country: gb
  • Test instrument designer/G1YWC
    • Electron Plus
Re: AC to DC voltage mirror for reference?
« Reply #5 on: August 06, 2021, 11:20:32 am »
What level of accuracy? Peak AC or RMS?
https://electron.plus Power Analysers, VI Signature Testers, Voltage References, Picoammeters, Curve Tracers.
 

Online wraper

  • Supporter
  • ****
  • Posts: 17610
  • Country: lv
Re: AC to DC voltage mirror for reference?
« Reply #6 on: August 06, 2021, 11:27:30 am »
For measurement you don't normally outright rectify high voltage and smooth it. It should be a voltage divider followed by precision rectifier. You will need to add true RMS to DC converter if you want to measure RMS voltage for different waveforms.
https://circuitdigest.com/electronic-circuits/half-wave-and-full-wave-precision-rectifier-circuit-using-op-amp
 


Share me

Digg  Facebook  SlashDot  Delicious  Technorati  Twitter  Google  Yahoo
Smf