Hi guys
I'm a EE student on placement and I've just taken over an existing power supply design that was never EMC tested. We are now wanting to put the design into a system that needs to be certified for EMC class A (EN 55032 CISPR 32). I took the system to the EMC test house the other day for some pre-compliance testing and it failed, miserably.
We determined that it was the AC/DC power supply that was the source because the system was still failing with just the power supply in the test rack.
We are using a PFE500SA-48 from TDK-Lambda as the main power module and have used the same supporting passives as they used for there in house verification. (See attached schematic).
Some notes from the pre-compliance:
- It failed both emission and immunity
- When we increased the size of the earthed chassis the results were worse
- It was failing at around 30MHz (Ive attached some results)
- It was broadband interference
Any experience would be appreciated.
Thanks
« Last Edit: February 07, 2020, 10:34:56 am by fordj06 »
Online moffy
Re: AC/DC 500W Supply EMC Issue's
« Reply #1 on: February 07, 2020, 11:51:54 am »
Have you tried a suitable ferrite  in series with the mains cable to attenuate the 30MHz etc?
Offline poorchava
  • Troll Cave Electronics!
« Reply #2 on: February 07, 2020, 02:25:26 pm »
Am I missing something or you don't ahve a capacitor between primary and secondary ground? Ie a way for interferences to close the loop. you could try adding a small (eg 4.7n y1 type) capacitor between grounds.
Offline T3sl4co1l
    • Seven Transistor Labs
« Reply #3 on: February 07, 2020, 02:39:04 pm »
Probably do this.
L1 probably isn't doing much.
What's conducted look like?
Seven Transistor Labs, LLC