PFC for anything with a SMPS inside is more to reduce harmonics in the neutral in the 3 phase distribution system. As the neutral typically is a thinner cable ( as it only has to handle the difference currents in the system, so can be smaller than the phase conductors in a supply) the extra harmonics tend to add up and overload it. Thus the need to reduce harmonics of the mains in a SMPS.
With inductive loads like transformers and motors you can add either a simple capacitive correction , or for larger transformers with a diode rectifier you add a series LC circuit tuned to 3 times mains frequency, to reduce those harmonics. Alternatively you use a ferroresonant transformer, which provides enough extra leakage inductance to isolate the power factor.
The power companies ( and large industrial users) have to add power factor correction to the supply side so this is not reflected down the power transmission lines, so as to reduce RF emission from the lines. Thus they also have power factor compensation capacitor banks, harmonic trap filters and synchronous capacitors in the power yards so as to keep the power factor over 0.9 lagging with only low levels of harmonics on the incoming feeds. This is a non billable power consumption, so they ideally want to keep this loss as low as possible.